Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Lucene indexing
Advanced server configuration
Configuring EcoStruxure IT Advisor for the advanced user
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
This setting is only to be used if the Data Center Operation client shows "inconsistent/ghost" data in the equipment browser after a search.
How to end up in a situation where the client shows inconsistent/ghost data
In some cases we have seen the Data Center Operation client display "inconsistent" data in the equipment browser. The way this can occur is, if i.e. a 2 day old backup is restored, then the user will be able to see/search for data created for the past 2 days, even though the backup does not hold this data.
Errors can occur if the user tries to modify these "inconsistent" data.
How to re-generate search indexes
In order to get rid of the inconsistent data, the Lucene search indexes needs to be deleted and re-generated.
Steps to be performed for a server:
In the file /etc/isx-operations/config add the line: ISXO_LUCENEINDEX_DELETE_ON_STARTUP=1 (1 means - delete , 0 means - do not delete )
stop the server
start the server
During startup: verify that the /data/lucene/indexes directory disappears for a while during the server startup.
When server is started: verify that the /data/lucene/indexes directory is available and has subdirectories.
It will take 15 min before the search indexes are started to be re-generated, and a rough estimate for when it is finished is 1 min. for each room in the solution. (i.e. 50 rooms = 50 min + 15 min. startup time.)
Note: With the above setting the server will always re-generate the indexes every time its restarted.
How to keep the indexes
Steps to be performed for a server:
In the file /etc/isx-operations/config make sure you have the following setting: ISXO_LUCENEINDEX_DELETE_ON_STARTUP=0 (1 means - delete , 0 means - do not delete )
stop the server
start the server
During startup: continuously verify that the /data/lucene/indexes directory is available and has subdirectories - do that until the server is started.
When server is started: verify that the /data/lucene/indexes directory is available and has subdirectories.