Vijeo Citect 7.3x upgradation to Plant SCADA 2023

AVEVA Plant SCADA Forum

A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Vijeo Citect 7.3x upgradation to Plant SCADA 2023
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
olivier_vallee
Commander olivier_vallee
34
Oncom
Commander Oncom
6
Kien_Mac
Lieutenant JG Kien_Mac Lieutenant JG
2
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to AVEVA Plant SCADA Forum
Start a Topic
Solved
Mehak
Lieutenant Mehak
Lieutenant

Posted: ‎2024-04-18 11:23 PM

0 Likes
5
3383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-18 11:23 PM

Vijeo Citect 7.3x upgradation to Plant SCADA 2023

Hi Everyone,

I want to upgrade my Vijeo Citect 7.3x to Plant SCADA 2023. My current point count is 15000. Kindly suggest the part number and suitable Plant SCADA 2023. The USB serial key is 0480-32650

Thank You in advance

Labels
  • Labels:
  • Plant SCADA Runtime
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
olivier_vallee
Commander olivier_vallee
Commander

Posted: ‎2024-04-22 05:08 PM

In response to Mehak
0 Likes
0
3297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-22 05:08 PM

That license allows you to run a Server/Client role with up to 10 connectivity clients attached (e.g. CTAPI or OPC clients). 

What is important is the version the license is able to run. When I put your key number into the GCS license tool, it says that this license is out of support and is only able to run v7.30 product.

Getting the key back into support will allow you to update the key to run the latest software (2023 R2 / v8.50).

Please get in contact with your distributor to discuss the options of getting this key back into support.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Kien_Mac
Lieutenant JG Kien_Mac Lieutenant JG
Lieutenant JG

Posted: ‎2024-04-22 08:25 PM

In response to Mehak
0 Likes
0
3298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-22 08:25 PM

Full License means you can run as a Full Server IO/Alarm/Trend/Report.
Connectivity (API/OPC) means you can connect upto 10 ctAPI / OPC Connections
Drivers All means you are licensed fto use all drivers.
Networking allowed means you can connect View/Control Clients to the Server using this license.

Kien Mac
Technical Solutions Consultant

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
olivier_vallee
Commander olivier_vallee
Commander

Posted: ‎2024-04-21 03:00 PM

0 Likes
0
3322
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-21 03:00 PM

Hi @Mehak,

I'd recommend reaching out to your AVEVA Sales representative (or Distributor) to get this key back into support. This will allow you to run the latest version and receive monthly software patches.

The latest version of AVEVA Plant SCADA is 2023 R2. The "Installation Guide" PDF on the ISO/ZIP also has a section on upgrading with all the details on how it can be done.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Kien_Mac
Lieutenant JG Kien_Mac Lieutenant JG
Lieutenant JG

Posted: ‎2024-04-21 05:09 PM

0 Likes
0
3340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-21 05:09 PM

Hi Mehak,

There has been step changes to Point Counts to align all AVEVA HMI/SCADA.

* 75,150,500 -> 1K
* 1500 -> 2.5K
* 5K -> 10K
* 15K, 50K -> 100K
* Unlimited.

If an end user is in current support or get back into CF Support, they would have access to update their USB keys to the latest version via AVEVA License Website.
https://softwaresupport.aveva.com/LicenseGenerator/Citect/#?selectedTab=LicenseGenerator

Otherwise, they will need to purchase an upgrade, which will entail upgrading these points at a cost.
Please contact your local SE representative to get a quotation.

Kien Mac
Technical Solutions Consultant
Reply

Link copied. Please paste this link to share this article on your social media post.

Mehak
Lieutenant Mehak
Lieutenant

Posted: ‎2024-04-22 05:36 AM

0 Likes
2
3317
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-22 05:36 AM

Thank You for the reply. I have 1 full license. 10 connectivity (API/OPC), 10 OLEDB connectors, drivers all supported, networking allowed, What does that mean? Please explain 

Thank You

Reply

Link copied. Please paste this link to share this article on your social media post.

olivier_vallee
Commander olivier_vallee
Commander

Posted: ‎2024-04-22 05:08 PM

In response to Mehak
0 Likes
0
3298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-22 05:08 PM

That license allows you to run a Server/Client role with up to 10 connectivity clients attached (e.g. CTAPI or OPC clients). 

What is important is the version the license is able to run. When I put your key number into the GCS license tool, it says that this license is out of support and is only able to run v7.30 product.

Getting the key back into support will allow you to update the key to run the latest software (2023 R2 / v8.50).

Please get in contact with your distributor to discuss the options of getting this key back into support.

Reply

Link copied. Please paste this link to share this article on your social media post.

Kien_Mac
Lieutenant JG Kien_Mac Lieutenant JG
Lieutenant JG

Posted: ‎2024-04-22 08:25 PM

In response to Mehak
0 Likes
0
3299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-22 08:25 PM

Full License means you can run as a Full Server IO/Alarm/Trend/Report.
Connectivity (API/OPC) means you can connect upto 10 ctAPI / OPC Connections
Drivers All means you are licensed fto use all drivers.
Networking allowed means you can connect View/Control Clients to the Server using this license.

Kien Mac
Technical Solutions Consultant
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore