A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
Posted: 2024-04-01 08:18 PM
Greetings.
Let me preface this by saying that I am entirely new to automation. Everything was going along fine until I ran into an old SEL connected by Modbus RTU over TCP/IP. I can pull the metering data just fine with MODNET. But the relay stores contact statuses as a single 16 bit with specific bits corresponding to different contacts. I have tried to change the driver to PwrModbus and configure the bitmask but I seem to failing entirely. Any help would be appreciated.
Posted: 2024-04-22 05:05 PM
Hi @Sergelenbat,
The PwrModbus is quite a complex driver, and is best configured using the Power SCADA Expert IDE and equipment tool with pre-defined templates for each device type.
Where would you like to use this bit extraction information? If on a page or in Cicode, you could simply use BITAND to extract the corresponding bit from the 16 bit integer.
E.g. to extract Bit 3 from Tag1, just use this (assuming Bit 0 is the first digital):
Tag1 BITAND 4
Hope this information helps.
Kind regards
Olivier
Hi @Sergelenbat,
Tag1 BITAND 4
Kind regards
Olivier