Plant SCADA 2023 Generic Protocol valid variable name

AVEVA Plant SCADA Forum

A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Plant SCADA 2023 Generic Protocol valid variable name
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
olivier_vallee
Lt. Commander olivier_vallee
28
Oncom
Commander Oncom
6
BevanWeiss
Spock BevanWeiss
2
RoozeeR
Lt. Commander RoozeeR Lt. Commander
2
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to AVEVA Plant SCADA Forum
Solved
macnite
macnite
Cadet

Posted: ‎2024-10-22 05:54 AM

0 Likes
1
484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-22 05:54 AM

Plant SCADA 2023 Generic Protocol valid variable name

I am using AVEVA Plant SCADA 2023 and trying to add a TIMESTAMP variable to an internal IO device known as DISK_DRIVE which uses the Generic protocol.  When I compile, I get the following error:

Bad IO Device variable (E2014)

Apparently this is because the Address "T1" is unacceptable for a TIMESTAMP data type in the generic protocol, but I can't find a reference that tells me what an acceptable address is for that data type in that protocol.  Where do I find a reference which will tell me what I can use?

Labels
  • Labels:
  • Plant SCADA Studio
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2024-10-23 08:41 PM

0 Likes
0
466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-23 08:41 PM

Hi @macnite, 

Variable Tags don't support the data type "TIMESTAMP". This is a data type for use in Cicode. Please see the Cicode reference for variable data types here:

https://docs.aveva.com/bundle/plant-scada/page/1130160.html

 

If you open up the file \Plant SCADA\Bin\Generic.dbf it contains the schema for the generic protocol address format (see extract):

TEMPLATE COMMENT
D%U Digital
I%U Integer
R%U Real
L%U Long
S%U String
DIGITAL%U Digital
INT%U Integer
REAL%U Real
LONG%U Long
STRING%U String

 

I think can safely define this tag as a LONG, say "L1" and it will compile.

You should then be ok to use this Generic DISK device variable within Cicode in the place that requires TIMESTAMP values, since Cicode will automatically convert the LONG datatype into the expected TIMESTAMP datatype for you. See this section for more information:

https://docs.aveva.com/bundle/plant-scada/page/1130158.html

Kind regards

Olivier

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Reply 1
olivier_vallee
Lt. Commander olivier_vallee
Lt. Commander

Posted: ‎2024-10-23 08:41 PM

0 Likes
0
467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-23 08:41 PM

Hi @macnite, 

Variable Tags don't support the data type "TIMESTAMP". This is a data type for use in Cicode. Please see the Cicode reference for variable data types here:

https://docs.aveva.com/bundle/plant-scada/page/1130160.html

 

If you open up the file \Plant SCADA\Bin\Generic.dbf it contains the schema for the generic protocol address format (see extract):

TEMPLATE COMMENT
D%U Digital
I%U Integer
R%U Real
L%U Long
S%U String
DIGITAL%U Digital
INT%U Integer
REAL%U Real
LONG%U Long
STRING%U String

 

I think can safely define this tag as a LONG, say "L1" and it will compile.

You should then be ok to use this Generic DISK device variable within Cicode in the place that requires TIMESTAMP values, since Cicode will automatically convert the LONG datatype into the expected TIMESTAMP datatype for you. See this section for more information:

https://docs.aveva.com/bundle/plant-scada/page/1130158.html

Kind regards

Olivier

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login