A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-07 12:01 AM
Hi everyone,
I'm trying to make a drop-down list of text items that operator can select one of them by Ci.Combobox.
I can create a text box includes all items but when clicking on one specific item, the selected item isn't returning.
Anyone had the same issue?
https://www.se.com/in/en/faqs/FA59/
This link is showing a sample but not working!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-10 06:26 PM
Hi Payam,
I just tried the code you link, and added a line to show the selection at the end. It works for me. I wonder whether you are pressing the cross at the top right corner to close the form? This will cancel the selection. To accept the selection on that form, you need to press "enter". Normally such a form would also include an OK and Cancel button as well.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-10 06:26 PM
Hi Payam,
I just tried the code you link, and added a line to show the selection at the end. It works for me. I wonder whether you are pressing the cross at the top right corner to close the form? This will cancel the selection. To accept the selection on that form, you need to press "enter". Normally such a form would also include an OK and Cancel button as well.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-10 06:28 PM
Also, a solution with ci.combobox would be a completely different (arguably better) solution.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-10 06:44 PM
Thanks for the reply.
The problem was solved and it's working now.
The main issue was returning the selected item that needs another internal tag to save the selected item and RETURN it at the end to the main program.
Many thanks for your time.