A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-06-05 02:51 AM
Can we connect one citect scada client to more than one citect server SCADA at the same project? (each server connect to different PLC at different site at different town)
Recently my client ask to connect all of their citect SCADA computer server which is located in a different site at different town into one citect SCADA client (one computer) which is going to be located at headquarters office. Is it possible to do this with citect SCADA and how to do it?
any one ever tried something like this before
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-06-05 06:18 AM
Halo Pak @adrianS ,
-sebetulnya forum ini khusus berbahasa indonesia lho pak π jadi sangat boleh untuk menggunakan bahasa indonesia.
sangat bisa pak. ini salah satu kelebihan dari Citect SCADA. fitur ini disebut Clustering dengan Global Client...
jadi pak Adrian cukup tambah 1 client lagi, dimana di client tersebut bisa di buat 1 project baru dengan meng-include kedua project di server1 dan Server2. dengan cara ini, Global Client akan mendapatkan akses ke kedua Server.
sebagai catatan... di dalam kedua project tidak boleh ada tag-name yang sama.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-06-07 09:25 PM
Halo Pak Oncom
Terima kasih untuk infonya, apakah terdapat dokumen yang menunjukan cara untuk mengkonfigurasi cluster sampai variable tag di client multi server-nya pak?
"sebagai catatan... di dalam kedua project tidak boleh ada tag-name yang sama."
Untuk tag name yang tidak boleh sama di tiap project ini apakah maksudnya tag SCADA nya atau tag dalam PLC nya pak?
Terima kasih
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-06-08 01:21 AM
saya kurang tau pasti ada dokumen nya atau tidak, tapi saya coba cari, jika ketemu nanti saya post disini.
sebenarnya cukup simple, cukup dibedakan nama clusternya, kemudian kedua projectnya di include dalam 1 project baru.
untuk tag yang tidak boleh sama, maksudnya adalah tagname di Citect SCADA nya antara Server 1 atau Server 2.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-06-12 05:06 AM
Halo Pak Oncom
Beberapa hari ini ada team kami yang mencoba untuk mengconfigurasi client untuk terhubung dengan 2 server di 2 komputer yang berbeda pak. Untuk percobaan ini kami menggunakan citect server dan client versi 7 pak.
Pada percobaan kami ini kami membuat 2 client dalam 1 project yang mana kedua client ini kami hubungkan ke 2 IP server yang berbeda. Saat kamiberusaha mengconectkan client kami dengan 1 server, client kami dapat dengan mudah terhubung ke kedua server secara bergantian (dengan mengubah computer setup wizard tiap kami mengubah server yang akan dihubungkan). Tetapi apabila kami mencoba menghubungkan client dengan 2 server secara bersamaan, client kami selalu gagal berkomunikasi dengan kedua server pak. Client kami selalu menunjukan tulisan '#com' di semua tag kami pak.
Berikut ini kami berikan screen shoot dari settingan client dan IO server kami:
Apakah ada yang salah/ kurang dalam konvigurasi kami pak?
Dengan konvigurassi ini kami dapat terhubung (tanpa error) dengan kedua server secara bergantian, tetapi bila menghubungkan dedngan kedua server bersamaan selalu lost connection sat run time di jalankan (padahal tidak ada error yang terdeteksi)
Kalau ada data lain yang masih perlu kami lampirkan bisa infokan langsung saja pak, akan kami kirimkan juga kalau diperlukan.
Mohon bantuannya pak
Terima kasih