Citect Modnet initvariable for 32bit-only devices
AVEVA Plant SCADA Forum
A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Citect Modnet initvariable for 32bit-only devices
olivier_vallee
Commander olivier_vallee
34
Oncom
Commander Oncom
6
Kien_Mac
Lieutenant JG Kien_Mac Lieutenant JG
2
Citect SCADA
Back to AVEVA Plant SCADA Forum
kor
Ensign kor
Ensign
Posted: ‎2023-02-04 09:33 AM
3077
I have a problem with connect to Citect  Modbus device ( network analyser ), this particular device allow only 2 and multiply 2 length readouts for registers. All request for 1 or odd length registers will provide exception code because all device memory is 32 bit organised.
In the MODNET I can't force use 2 register (long ) readout for init variable, in documentation there is present only 'initvariable' parameter but it's related to choose between (holding/input registers an so one ) but to ti force read at least 2 word instead 1 as Modnet driver does.
There is a way to force init device request as 2 word length?
  • Communication Drivers
Replies 7
PV_DAQ
Ensign PV_DAQ
Ensign
Posted: ‎2023-02-10 10:33 PM
3022
I ran into a flowmeter that defaulted to 32 bit floating point memory architecture, similar to what you describe for the network analyzer, but discovered that a configuration variable allowed for the choice of "Modicon standard", the conventional Modbus memory architecture with standard 16 bit word registers: Integers for 16 bit single word registers, floats need 2 contiguous registers.
Can the network analyzer be configured for standard Modbus operation?
kor
Ensign kor
Ensign
Posted: ‎2023-02-11 01:17 AM
In response to PV_DAQ
3018
Unfortunately, my analysers has only the one data and memory format 32bit
PV_DAQ
Ensign PV_DAQ
Ensign
Posted: ‎2023-02-12 05:41 AM
In response to kor
Can you post a link to the Modbus documentation for the device?
kor
Ensign kor
Ensign
Posted: ‎2023-02-12 10:52 PM
Please find attached here: Frer modbus docs
PV_DAQ
Ensign PV_DAQ
Ensign
Posted: ‎2023-02-13 08:12 AM
2965
I don't understand exactly what your problem is. Modbus functionality appears to be conventional on this slave device.
Some variables are 16 bit, single Modbus register integers, some are 32 bit, two Modbus register long integers.
The slave supports FC03 to read Holding registers and FC16(h) to write to holding registers.
The slave does not allow a read or write to only half of a multi-register variable, which is for your own good, so you don't get meaningless data.
Which variable (register number) are you trying to read or write that you can't?
kor
Ensign kor
Ensign
Posted: ‎2023-02-13 09:43 AM
All variables are 32 bit, as I've wrote analyser will't answer if we've asked about one register from 32 bit pair.
PV_DAQ
Ensign PV_DAQ
Ensign
Posted: ‎2023-02-13 10:40 AM
 I can't help if you don't provide actual details, sorry.