surge protection not working on Smart-UPS SRT 5000s - why?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • surge protection not working on Smart-UPS SRT 5000s - why?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
jerryku7
jerryku7
Cadet

Posted: ‎2023-04-26 11:38 AM . Last Modified: ‎2023-04-26 12:01 PM

0 Likes
2
566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-26 11:38 AM . Last Modified: ‎2023-04-26 12:01 PM

surge protection not working on Smart-UPS SRT 5000s - why?

My company uses the Smart-UPS SRT 5000 to protect network equipment. Recently, at three different buildings, we have seen thousands of dollars worth of equipment be destroyed by power surges. The equipment was supposed to have been protected by the UPSs but was not.  Can APC/Schneider support explain why?

 

To elaborate...   each building has network equipment cabinets with two 220V AC outlets, two SRT 5000s, ,two APC PDUs, and three network switches (each switch has two power supply units aka PSUs).

 

Each SRT 5000 plugs into one of the AC outlets.

Each PDU is plugged into one of the UPSs.

For each network switch, one PSU is plugged into one of the PDUs, and the other PSU is plugged into the other PDU.

 

Each building was fully shut down.  Main utility and backup generator power were completely turned off.

All UPS devices in the network cabinets were fully unplugged from the 220V AC outlets mentioned above.

Then, when main utility and backup generator power was restored, the UPS devices were reconnected to the 220V AC outlets.

 

For all three buildings, some network equipment was destroyed, presumably by power surges. The devices do not boot up anymore and must be RMA'ed or thrown away. Any theories as to why the destruction occurred at all?

 

From reading this post: https://community.se.com/t5/APC-UPS-for-Home-and-Office-Forum/Why-is-my-apc-Ups-Joules-rating-so-low...

 

BillP said:

 

"Our products are designed to redirect the surge back to ground instead of absorbing it and incorporate a let through voltage, which is the maximum transient voltage the attached equipment will be subjected to above the normal RMS voltage. Any remaining voltage is redirected to ground."

 

So why did equipment still get destroyed?

 

also..

 

1) Reading Rau_APC's posts in https://community.se.com/t5/APC-UPS-for-Home-and-Office-Forum/UPS-surge-protection-status/m-p/328775 ...the UPSs do not have a way to report that the surge protection is no longer working.  But does my company have to worry about the MOVs inside the UPSs depleting? And becoming too old to be functional?

 

In other words, for the UPSs involved in the three cases mentioned above, is the surge protection now no longer working for these units since a surge event (probably) happened?

 

2) Our UPSs do not have their chassis ground screws grounded to anything. I assume this does not matter in regards to the network equipment being destroyed. But is that correct? I assume that the chassis ground screws are to protect people from being electrocuted when touching the metal surface of the UPS, if a wiring fault occurs within the UPS. So it would have nothing to do with surge damage..

 

 

 

 

 

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-05-01 07:28 AM

0 Likes
1
528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-01 07:28 AM

@jerryku7 

 

We cannot explain what may have happened with out an investigation. Your UPSs are covered by the equipment protection policy https://www.apc.com/us/en/support/equipment-protection-policy/ 

You should contact local support and they will be happy to assist you. 

 

Local support contact information will be found at this link.

https://www.apc.com/us/en/support/contact-us/index.jsp

You may need to change the region in the upper left of the contact us web page. 

Reply

Link copied. Please paste this link to share this article on your social media post.

jerryku7
jerryku7
Cadet

Posted: ‎2023-05-01 07:36 AM

In response to BillP
0 Likes
0
526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-01 07:36 AM

Our UPSs are 208V so i don't think we're covered

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of