firmware update for UPS Network Management Card 2 (Smart-UPS SRT 3000) - failed

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • firmware update for UPS Network Management Card 2 (Smart-UPS SRT 3000) - failed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
qqblog
qqblog
Cadet

Posted: ‎2023-06-06 09:48 PM

0 Likes
3
4087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-06 09:48 PM

firmware update for UPS Network Management Card 2 (Smart-UPS SRT 3000) - failed

Current Version - ID1010UPS 05.3

 

i downloaded and extracted. i can see below files

https://www.apc.com/hk/en/product/AP9630/apc-ups-network-management-card-2/

 

apc_hw05_aos712_sumx712_bootmon109
sumx_712_frFrdeDeitItesEsptBr.lpk
sumx_712_frFrruRuzhCnjaJakoKo.lpk

 

i have tried uploading the zipfile or each of the unzipped files. all failed to update firmware.

 

pls advise

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2023-06-06 11:35 PM . Last Modified: ‎2023-06-06 11:36 PM

0 Likes
2
4082
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-06 11:35 PM . Last Modified: ‎2023-06-06 11:36 PM

Hello Qqblog 

 

The firmware on the network card and the firmware on the UPS are two separate and different firmwares. Looking at you "current version", you are looking at UPS firmware, whereas the firmware files you are referring to are for a network card. So, it fails for a good reason.

 

If you have a network card in the UPS, upgrading that to latest release is very often a good idea, as security and feature updates happen at a regular interval. And, if something fails during a firmware upgrade, recovering the card is almost always possible.

 

The UPS firmware is different, updates are not as frequent, and the changes made in the firmware often address specific issues. Rule of thumb for the UPS firmware is to leave it as is, unless specifically instructed to upgrade by our support to fix a specific issue.

 

I hope the above makes sense.

 

Best regards

Tonny

Reply

Link copied. Please paste this link to share this article on your social media post.

qqblog
qqblog
Cadet

Posted: ‎2023-06-06 11:53 PM

In response to TonKei
0 Likes
1
4079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-06 11:53 PM

thank you for your reply. i would like to update the mgt card firmware. is below the correct location?

 

qqblog_0-1686120764469.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

TonKei
Lieutenant TonKei Lieutenant
Lieutenant

Posted: ‎2023-06-07 12:06 AM

In response to qqblog
0 Likes
0
4076
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-07 12:06 AM

Hello Qq

 

Nope!

 

I would suggest taking a look at this FAQ document, detailing the different update options that are available -> https://www.apc.com/ie/en/faqs/FA156047/

 

As to the firmware to use, this depends on the generation of card you have installed in your UPS

The files you mention are for the second generation of cards (AP9630/AP9631), if you have a 3. gen. (AP9640/AP9641) the latest firmware is available here -> https://download.schneider-electric.com/files?p_Doc_Ref=APC_NMC3_SU_24011_EN&p_enDocType=Firmware&p_...

 

Best regards

Tonny

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore