Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
What is the correct setting for Battery Bank Capacity on the Conext SW 4048 with Two 4 battery banks of 250AH batteries
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-2312:26 PM
What is the correct setting for Battery Bank Capacity on the Conext SW 4048 with Two 4 battery banks of 250AH batteries
I am receiving conflicting information on what I should set the Batt Capacity (Under charger Settings) on the Conext SW4048. I have a total of 8, 250ah batteries (two banks of 4).
One argument is: It should be 500ah given that there are two banks of 250ah
Another argument is: It should be 250ah given that is what each battery is
Still another argument is: It should be less than 250ah; because, I have a Midnite charge controller and that it does not play well with the Conext.
I appreciate your input on what I thought was a very basic question
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-2601:46 AM
hi, short answer is 500ah because they're 2 strings each of 48V, 250Ah.
long answer, from the basis of series and parallel connections, you're connecting 2 parallel strings of 250Ah, so in total it would be 500Ah and 48V would be maintained across the strings.
concerning the Midnite charge controller, I haven't worked with this before but I'll take it as any regular charge controller and you can still configure the system with the same amount of Ah. Just put the settings correctly on both of them (like your charging rate and voltages)