Two 40kW UPS's with ~100 servers - how to configure for redundancy?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Two 40kW UPS's with ~100 servers - how to configure for redundancy?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-25 10:24 PM . Last Modified: โ€Ž2024-03-19 03:36 AM

0 Likes
2
639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 10:24 PM . Last Modified: โ€Ž2024-03-19 03:36 AM

Two 40kW UPS's with ~100 servers - how to configure for redundancy?

Our server room has got approx ~100 servers and other associated equipment in it. We've currently got a single 40kW APC UPS maxed out at 99-102% load (I know, baaad idea). We've just put in place a second 40kW APC UPS to bring more power to the room give our forecasted growth. Each UPS is fed from a separate power source from the building. We had to route a new power feed through the building into our room to fuel the new unit.

So here is my question. What is the smartest way to distribute the load of all our servers? It would seem to make sense to have power available in each rack to both UPS units. Since each server has two power supplies, plug one into one UPS and the other into the other UPS. This provides redundancy. The problem is, however, that if one UPS were to go down, the remaining UPS could not pick up the load of the entire room - so does that make this method futile anyway?

The other option is to plug half the servers into one UPS and the other half into the other UPS.

Just not sure which option makes the most sense. We were trying to avoid the situation in which we have some racks running off one UPS and some racks running off the other. so in a power failure it gives us more things to manage. I had hoped the two could work in tandem as one complete power source, but that does not appear to be the case.

Any thoughts would be greatly appreciated.

Labels
  • Labels:
  • Server Room & Data Center Design Best Practices
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
cmarler_apc
Lieutenant JG cmarler_apc
Lieutenant JG

Posted: โ€Ž2021-06-25 10:24 PM . Last Modified: โ€Ž2024-03-19 03:36 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 10:24 PM . Last Modified: โ€Ž2024-03-19 03:36 AM

Hey Road Hog, you can't make an 80KW UPS out of two 40KW UPS unless they can operate in parallel. It requires phase synchronization circuitry that is too expensive for this product line. They won't work in tandem as one complete power source, sorry.

One option you didn't mention is to distribute standard utility power to all your racks, to one side of the dual power supply servers B feed. Then feed the other side of the servers dual power A feed from UPS. Feed half your racks from one UPS and half your racks from the second UPS. Since you are thinking dual UPS, dual cords to plan for a UPS failure, it will give you the ability to spread your UPS risk around.

..now to make things even more complicated, well, you are doing power work anyway, might as well do it right.... if you decide this option works for you, use 3-phase rack power distribution for the new utility power B feed. That way you can plug one server's power supply into "house power" phase 1, and one power supply into UPS power phase 2... alternate phases as you deploy this power distribution strategy and you will have gained phase redundancy.

You'll also be positioned to assign physical and logical redundant servers to applications and have them on separate UPS, there's some brownie points for you.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: โ€Ž2021-06-25 10:24 PM . Last Modified: โ€Ž2024-03-19 03:36 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 10:24 PM . Last Modified: โ€Ž2024-03-19 03:36 AM

100%! I hope you have a really good generator ๐Ÿ™‚
I would suggest you to utilize a hybrid approach. That is do not load balance all of your equipment, since you do not want to overload your 1st UPS if the 2nd fails, especially if you are anticipating growth.
You would have 2 PDUs in each rack, connected to the different UPSs. First, identify your critical equipment, I am sure you already done that. The critical equipment would be connected to both of the PDUs that gives you power redundancy. The low priority equipment should be connected to only one UPS, which you will "round-robin" between your UPSs, keeping power draw in mind. One thing to note is that servers utilizing both power supplies actually pull more power than if using only one power supply. This should give you about 60% utilization on your UPSs, when both are online. That number will go up if a UPS becomes unavailable. If you do not have low-priority equipment, you should consider buying more battery cabinets. Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

cmarler_apc
Lieutenant JG cmarler_apc
Lieutenant JG

Posted: โ€Ž2021-06-25 10:24 PM . Last Modified: โ€Ž2024-03-19 03:36 AM

0 Likes
0
642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 10:24 PM . Last Modified: โ€Ž2024-03-19 03:36 AM

Hey Road Hog, you can't make an 80KW UPS out of two 40KW UPS unless they can operate in parallel. It requires phase synchronization circuitry that is too expensive for this product line. They won't work in tandem as one complete power source, sorry.

One option you didn't mention is to distribute standard utility power to all your racks, to one side of the dual power supply servers B feed. Then feed the other side of the servers dual power A feed from UPS. Feed half your racks from one UPS and half your racks from the second UPS. Since you are thinking dual UPS, dual cords to plan for a UPS failure, it will give you the ability to spread your UPS risk around.

..now to make things even more complicated, well, you are doing power work anyway, might as well do it right.... if you decide this option works for you, use 3-phase rack power distribution for the new utility power B feed. That way you can plug one server's power supply into "house power" phase 1, and one power supply into UPS power phase 2... alternate phases as you deploy this power distribution strategy and you will have gained phase redundancy.

You'll also be positioned to assign physical and logical redundant servers to applications and have them on separate UPS, there's some brownie points for you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of