APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:20 AM . Last Modified: 2024-02-14 11:04 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:20 AM . Last Modified: 2024-02-14 11:03 PM
Hi Surendra,
AP7921 is based on our Network Management Card 1 (NMC1) technology which only allows (1) connection to each interface. There is no way to change this.
AP8941 is based on NMC2 technology which does now allow multiple user sessions of any type - web, telnet, SSH, etc except for local serial connection.
Any NMC1 device will operate the same way and any NMC2 based device will also operate the same as described above.
Side note: We created AP7921B which is AP7921B with an NMC2 inside of it so it is possible on that model to do multiple telnet sessions.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:20 AM . Last Modified: 2024-02-14 11:04 PM
Hi,
On 7/24/2017 1:18 AM, Surendra said:is there any firmware upgrade for allowing cuncurrent telnet sessions to the APC ?
No. The interface has been designed to allow only 1 Telnet session at a time. The reasoning is to prevent conflicting changed happening concurrently.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:20 AM . Last Modified: 2024-02-14 11:03 PM
Hi Bill,
thanks for the response, you mean to say there is no way to access concurrently this APC,
if that is the case then how it is enabled on other models like AP8941.
Thanks,
M.Surendra Kumar
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:20 AM . Last Modified: 2024-02-14 11:03 PM
Hi,
On 7/24/2017 11:13 AM, Surendra said:if that is the case then how it is enabled on other models like AP8941.
The AP8941 has a second generation network card embedded. The AP7921 has generation 1 embedded card.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 04:20 AM . Last Modified: 2024-02-14 11:03 PM
Hi Surendra,
AP7921 is based on our Network Management Card 1 (NMC1) technology which only allows (1) connection to each interface. There is no way to change this.
AP8941 is based on NMC2 technology which does now allow multiple user sessions of any type - web, telnet, SSH, etc except for local serial connection.
Any NMC1 device will operate the same way and any NMC2 based device will also operate the same as described above.
Side note: We created AP7921B which is AP7921B with an NMC2 inside of it so it is possible on that model to do multiple telnet sessions.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.