Symmetra PX Battery Bus voltage, how?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra PX Battery Bus voltage, how?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
ojfsdi
Ensign ojfsdi
Ensign

Posted: ‎2021-10-12 12:21 AM

0 Likes
4
2709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-12 12:21 AM

Symmetra PX Battery Bus voltage, how?

I noticed in the web interface of our symmetra px, battery voltage is listed as  214vDC.

 

Nominal Battery Voltage:192.2 VDC
Actual Battery Bus Voltage:214.2 VDC

 

But each battery back has 8x12v sla batteries.

 

8*12=96v right?  So how do they come up with 192 or 214v?

 

96*2=192.  So does this UPS use two battery modules in series to get 192v?  It so, should I keep the A &B Columns even, and c&d columns even to keep it running smoothly?  OR does the UPS monitor what bus needs a boost in voltage the most and use relays to change the DC bus its ok.

Labels
  • Labels:
  • Datacenter UPS
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-13 12:06 PM

In response to ojfsdi
0 Likes
1
2688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-13 12:06 PM

Hi,

 

A few additional comments based on your reply

 

 

 If a C module "fails" then its paired D module should be listed 'unavailable' or something, not merely "ok".

 

It actually will do this but it depends on the scenario. There are four ways in which the PX 10-160 will declare a battery as being in a fault condition.

 

  1.  A "wear out" condition. The UPS monitors the midpoint voltage of each battery pair on a shelf (AB / CD) and will declare the pair as being failed if the appropriate criteria is met.  This condition can only be detected when the UPS is running in battery operation.
  2.  The UPS monitors the discharge current from each battery pair. If the measured value is below a certain level the UPS will declare the pair as being failed. Each battery module is individually fused. The log files stored within the Intelligence Modules will record this as a blown fuse alarm (though technically we are not monitoring the fuse itself).
  3. Overtemperature. Each battery module contains a temperature sensor. If the measured temperature  of any battery module exceeds 140F (60C) then that individual battery will be declared as failed. This is the only scenario where you could see a "B" battery reporting as OK while its pair in the "A" position is reporting as failed. 
  4. Mixed battery. Schneider Electric sources the batteries for the PX from multiple vendors. Batteries must be installed in like pairs (A must match B and C must match D). There is a sticker on the front of the battery which will identify the type. Mixing batteries within a pair would not allow for proper fault monitoring on items 1 and 2 above hence the fault declaration. 

 

I would have at least labeled them A1, A2, B1, B2.

 

The batteries are labeled in this manner. Here is a screen capture from a Symmetra PX40 NMC. This is also available through  the display in a slightly different format.

 

2021-10-13_14-07-41.png

 
 

 

It sounds like shelves L1-L4 are one unit, and L5-L8 (in an 80kw system) are another, 

 

Yes, but not from an electrical perspective.  This is only how the monitoring works. The battery monitoring board present in the UPS can only monitor a maximum of 4 shelves. You'll find one of these boards in each Symmetra PX 40K and then 2 in each external battery cabinet. 

 

Are the bus bars fully rated?  in other words, if I had 1c, 1d, 2c, 2d, 3a, 3b, 4a, 4b all vacant, would the remaining cartridges on the right side of L1 and L2 balance out the left side of L3 and L4 without damaging the bus bar  between L2 and L3?

 

The bus bars are rated to handle the full current capacity of the system. By reducing the number of batteries you would be reducing your runtime. The load (while on battery) or the number of power modules (while online - charging current) is what would dictate the current draw. It would not be standard to install the batteries in incomplete shelves. 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-12 12:54 PM

0 Likes
3
2700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-12 12:54 PM

Hi,

 

The 214v is the float voltage level. The nominal voltage is 192vdc. As you have surmised the  batteries are connected in series to make 192vdc.  The "AB"  batteries make up the positive string and the CD batteries make up the negative. You can find a detailed description of the Symmetra PX batteries here: https://www.apc.com/us/en/download/document/SPD_AKAR-88TTJW_EN/

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ojfsdi
Ensign ojfsdi
Ensign

Posted: ‎2021-10-12 08:34 PM

In response to al_buffington
0 Likes
2
2692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-12 08:34 PM

Well.  I wish I had known that!  Sure does explain why cartridges that did not have a neighbor were always cold, even if they had been warm somewhere else previously.

 

It's a real shame that the web interface and front panel don't communicate that at all.  If a C module "fails" then its paired D module should be listed 'unavailable' or something, not merely "ok".

 

Interesting design choice.  I suppose necessary for their igbt approach.  but I would have at least labeled them A1, A2, B1, B2.  Or +a+b  -a -b.

 

It sounds like shelves L1-L4 are one unit, and L5-L8 (in an 80kw system) are another, though it's probably of little consequence if they're paralleled together.

 

Are the bus bars fully rated?  in other words, if I had 1c, 1d, 2c, 2d, 3a, 3b, 4a, 4b all vacant, would the remaining cartridges on the right side of L1 and L2 balance out the left side of L3 and L4 without damaging the bus bar  between L2 and L3?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

al_buffington
Lieutenant JG al_buffington Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-13 12:06 PM

In response to ojfsdi
0 Likes
1
2689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-13 12:06 PM

Hi,

 

A few additional comments based on your reply

 

 

 If a C module "fails" then its paired D module should be listed 'unavailable' or something, not merely "ok".

 

It actually will do this but it depends on the scenario. There are four ways in which the PX 10-160 will declare a battery as being in a fault condition.

 

  1.  A "wear out" condition. The UPS monitors the midpoint voltage of each battery pair on a shelf (AB / CD) and will declare the pair as being failed if the appropriate criteria is met.  This condition can only be detected when the UPS is running in battery operation.
  2.  The UPS monitors the discharge current from each battery pair. If the measured value is below a certain level the UPS will declare the pair as being failed. Each battery module is individually fused. The log files stored within the Intelligence Modules will record this as a blown fuse alarm (though technically we are not monitoring the fuse itself).
  3. Overtemperature. Each battery module contains a temperature sensor. If the measured temperature  of any battery module exceeds 140F (60C) then that individual battery will be declared as failed. This is the only scenario where you could see a "B" battery reporting as OK while its pair in the "A" position is reporting as failed. 
  4. Mixed battery. Schneider Electric sources the batteries for the PX from multiple vendors. Batteries must be installed in like pairs (A must match B and C must match D). There is a sticker on the front of the battery which will identify the type. Mixing batteries within a pair would not allow for proper fault monitoring on items 1 and 2 above hence the fault declaration. 

 

I would have at least labeled them A1, A2, B1, B2.

 

The batteries are labeled in this manner. Here is a screen capture from a Symmetra PX40 NMC. This is also available through  the display in a slightly different format.

 

2021-10-13_14-07-41.png

 
 

 

It sounds like shelves L1-L4 are one unit, and L5-L8 (in an 80kw system) are another, 

 

Yes, but not from an electrical perspective.  This is only how the monitoring works. The battery monitoring board present in the UPS can only monitor a maximum of 4 shelves. You'll find one of these boards in each Symmetra PX 40K and then 2 in each external battery cabinet. 

 

Are the bus bars fully rated?  in other words, if I had 1c, 1d, 2c, 2d, 3a, 3b, 4a, 4b all vacant, would the remaining cartridges on the right side of L1 and L2 balance out the left side of L3 and L4 without damaging the bus bar  between L2 and L3?

 

The bus bars are rated to handle the full current capacity of the system. By reducing the number of batteries you would be reducing your runtime. The load (while on battery) or the number of power modules (while online - charging current) is what would dictate the current draw. It would not be standard to install the batteries in incomplete shelves. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ojfsdi
Ensign ojfsdi
Ensign

Posted: ‎2021-10-14 04:14 PM

In response to al_buffington
0 Likes
0
2666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-14 04:14 PM

Interesting.  Every fault I've seen has been a single battery module.  And they were all, obviously thermal (overheat) related.

 

Once I've gotten some of the older cells out and new ones in their place I'm going to to a runtime cal, and then schedule a weekly test to suss out any worn out pairs.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of