Launch of Consumer/Home Owner registration process!
We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Symmetra PX 80kVa Recharge Draw
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-2208:07 AM
Symmetra PX 80kVa Recharge Draw
We have a 80kVa Symmetra PX unit with 2 battery frames filled. We usually have a load of around 30%, we don't push it very hard. Most we ever had loaded on it was about 40%.
We had a recent outage and the output breaker on our generator tripped and we're doing some calculations to see if the building load might have tripped it or if it's possible that there was a ground fault (it was raining hard).
The breaker we have for this unit at the panel is a 150amp at 480v which is what is specified in the installation guide. What is a reasonable draw for this unit when the generator is running and the UPS is recharging it self while also serving our current load profile?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-2503:55 AM
Hi,
150A is the correct breaker value if you have a 480V source feeding a PDU w/ bypass that is stepping down the voltage to 208. The battery charging power for the PX80 is 1kw per power module. The typical draw would be whatever your load is plus 9kw (this assumes you have a redundant power module). There is an option to disable battery charging while the generator is running (through a dry contact) but this would require field service involvement to enable. This feature is only available with intelligence module firmware version 17.0 and higher. I hope this answers your question.