Symmetra LX Intelligence Module faults won’t go away? A fix.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX Intelligence Module faults won’t go away? A fix.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
djb_rh
Crewman djb_rh
Crewman

Posted: ‎2023-10-31 04:23 PM

0 Likes
0
1248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-31 04:23 PM

Symmetra LX Intelligence Module faults won’t go away? A fix.

So I’m new around here, but I’ve had a pair of Symmetra LX’s for going on 20 years now that I’ve been maintaining (just recently started posting in the battery thread about how to refurb those at home, many thanks to those who published that info originally!).

 

I’ve searched and not found anything about this, but I thought it worth mentioning that a few years ago I had my first intelligence module fail. It started slowly with errors that it wasn’t working right, then it would apparently come back after being on the other one for a while. It was infrequent at first and since those are redundant I kinda let it go. But it started happening enough that I found an NOS module on eBay and popped it in. I decided to open up the bad one thinking it might be bad electrolytic capacitors. Lo and behold, I could see at least one was vented with another one looking sketchy.

 

I don’t remember exactly how many there were, I think four or five, on the entire thing. I simply got the values and ordered up five sets of them from Digikey. Then I replaced the ones in the bad module and put it back in my UPS in place of the NOS one. I let it cook for a month which was MORE than enough time for the fault to come back given how it was acting before the swap and no errors. So then I swapped the capacitors on the NOS one (they probably had some time left in them, but they do die due to age *and* use) and swapped it in for one of the other originals and started swapping caps on them all one at a time until I did them all.  Haven’t had another error in many years since.

 

I know that’s not *specific* info, but anyone who has the skills to solder and is comfortable working on something like this can easily pop one open and figure out the handful that you need to swap. But if anyone has detailed questions about it, I’ll do my best to answer. Those capacitors are cheap and only took a few minutes to change, so well worth it over buying new modules that probably won’t last THAT long either. I’m gonna keep these things cobbled together as long as I can!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore