Smart-UPS SRT 5000 Cartdridge not installed after self-test

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SRT 5000 Cartdridge not installed after self-test
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
asanchezUA
asanchezUA
Cadet

Posted: ‎2025-02-05 06:33 AM

0 Likes
2
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-05 06:33 AM

Smart-UPS SRT 5000 Cartdridge not installed after self-test

Hi everyone,

 

I have a Smart-UPS SRT 5000 that reports Cartridge 1 not installed and then installed after running a self-test. The Cartidge is new and was installed last month.

 

Any ideas?

 

Thank You!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-10 05:49 AM

1 Like
1
694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-10 05:49 AM

Hello,

if the RBC is newly replaced, ensure to update the battery replacement date from the display or NMC and run self test and ensure the UPS firmware is updated to the latest version and the batteries connectors are securely plugged

 

Generally. ensure the External Battery Pack cable is securely connected, if applicable. , ensure both the External Battery Pack power and communication cables are securely connected. Perform a self-test with at least 500W load.

When there is a Check Battery Cable alarm present, usually it is an indication that one of the battery cables from the XBPs is having an issue.
In a low number of cases, it sometimes could indicate a fuse is open inside the UPS, one of the XBPs, or XBP the battery cartridges. To isolate this, remove all the XBPs and just have the UPS standalone to see if there is a fault present. UPS fault status should change if there is one at the UPS. If a fault is present, proceed with a. If not, proceed with b.
If “Internal Battery Disconnected” error pops up, it sometimes indicates the fuse is open (either in the battery module or the UPS itself). Try to install a known good battery in the UPS (without any XBPs connected) to see if that fault clears. If it does not, then it is a good indication the UPS fuse is open and the UPS needs to be replaced.
To isolate which XBPs fuse is open (or just having an issue to begin with), connect each XBP (with a known good battery installed) along with the UPS to see what error message pops up. It is very rare fuses are open in every single XBP along with the UPS. Keep attaching XBPs to see when the error message pops up and to see if the fuse is open in the XBP itself. Replace necessary equipment.
If any of these issues persists, perform a UPS firmware upgrade to the latest firmware revision available in FA279197 .

 

Regards,

 

Karim

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-10 05:49 AM

1 Like
1
695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-10 05:49 AM

Hello,

if the RBC is newly replaced, ensure to update the battery replacement date from the display or NMC and run self test and ensure the UPS firmware is updated to the latest version and the batteries connectors are securely plugged

 

Generally. ensure the External Battery Pack cable is securely connected, if applicable. , ensure both the External Battery Pack power and communication cables are securely connected. Perform a self-test with at least 500W load.

When there is a Check Battery Cable alarm present, usually it is an indication that one of the battery cables from the XBPs is having an issue.
In a low number of cases, it sometimes could indicate a fuse is open inside the UPS, one of the XBPs, or XBP the battery cartridges. To isolate this, remove all the XBPs and just have the UPS standalone to see if there is a fault present. UPS fault status should change if there is one at the UPS. If a fault is present, proceed with a. If not, proceed with b.
If “Internal Battery Disconnected” error pops up, it sometimes indicates the fuse is open (either in the battery module or the UPS itself). Try to install a known good battery in the UPS (without any XBPs connected) to see if that fault clears. If it does not, then it is a good indication the UPS fuse is open and the UPS needs to be replaced.
To isolate which XBPs fuse is open (or just having an issue to begin with), connect each XBP (with a known good battery installed) along with the UPS to see what error message pops up. It is very rare fuses are open in every single XBP along with the UPS. Keep attaching XBPs to see when the error message pops up and to see if the fuse is open in the XBP itself. Replace necessary equipment.
If any of these issues persists, perform a UPS firmware upgrade to the latest firmware revision available in FA279197 .

 

Regards,

 

Karim

Reply

Link copied. Please paste this link to share this article on your social media post.

asanchezUA
asanchezUA
Cadet

Posted: ‎2025-02-11 06:11 AM

In response to KarimEissa
0 Likes
0
664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-11 06:11 AM

Thank you Karim! 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore