SSH from Fedora 41 to AP9631 fails: ssh_dispatch_run_fatal: error in libcrypto

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SSH from Fedora 41 to AP9631 fails: ssh_dispatch_run_fatal: error in libcrypto
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
aswen
aswen
Cadet

Posted: ‎2025-01-28 12:10 PM

0 Likes
4
2652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-28 12:10 PM

SSH from Fedora 41 to AP9631 fails: ssh_dispatch_run_fatal: error in libcrypto

Hi,

SSH to my AP9631 NMC fails with this error:

$ ssh -v apc-ups.my.net.work
OpenSSH_9.9p1, OpenSSL 3.2.2 4 Jun 2024
debug1: Reading configuration data /home/alex/.ssh/config
debug1: /home/alex/.ssh/config line 31: Applying options for apc-ups.my.net.work
debug1: /home/alex/.ssh/config line 108: Applying options for *.my.net.work
debug1: /home/alex/.ssh/config line 172: Applying options for *
debug1: Reading configuration data /etc/ssh/ssh_config
debug1: Reading configuration data /etc/ssh/ssh_config.d/20-systemd-ssh-proxy.conf
debug1: Reading configuration data /etc/ssh/ssh_config.d/30-libvirt-ssh-proxy.conf
debug1: Reading configuration data /etc/ssh/ssh_config.d/50-redhat.conf
debug1: Reading configuration data /etc/crypto-policies/back-ends/openssh.config
debug1: /etc/ssh/ssh_config line 57: Applying options for *
debug1: configuration requests final Match pass
debug1: re-parsing configuration
debug1: Reading configuration data /home/alex/.ssh/config
debug1: /home/alex/.ssh/config line 31: Applying options for apc-ups.my.net.work
debug1: /home/alex/.ssh/config line 108: Applying options for *.my.net.work
debug1: /home/alex/.ssh/config line 172: Applying options for *
debug1: Reading configuration data /etc/ssh/ssh_config
debug1: Reading configuration data /etc/ssh/ssh_config.d/20-systemd-ssh-proxy.conf
debug1: Reading configuration data /etc/ssh/ssh_config.d/30-libvirt-ssh-proxy.conf
debug1: Reading configuration data /etc/ssh/ssh_config.d/50-redhat.conf
debug1: Reading configuration data /etc/crypto-policies/back-ends/openssh.config
debug1: /etc/ssh/ssh_config line 57: Applying options for *
debug1: Connecting to apc-ups.my.net.work [172.17.255.240] port 22.
debug1: Connection established.
debug1: identity file /home/alex/.ssh/id_rsa type -1
(...)
debug1: Local version string SSH-2.0-OpenSSH_9.9
debug1: Remote protocol version 2.0, remote software version cryptlib
debug1: compat_banner: no match: cryptlib
debug1: Authenticating to apc-ups.my.net.work:22 as 'apc'
debug1: load_hostkeys: fopen /home/alex/.ssh/known_hosts2: No such file or directory
debug1: load_hostkeys: fopen /etc/ssh/ssh_known_hosts: No such file or directory
debug1: load_hostkeys: fopen /etc/ssh/ssh_known_hosts2: No such file or directory
debug1: SSH2_MSG_KEXINIT sent
debug1: SSH2_MSG_KEXINIT received
debug1: kex: algorithm: ecdh-sha2-nistp256
debug1: kex: host key algorithm: ssh-rsa
debug1: kex: server->client cipher: aes256-ctr MAC: hmac-sha2-256 compression: none
debug1: kex: client->server cipher: aes256-ctr MAC: hmac-sha2-256 compression: none
debug1: kex: ecdh-sha2-nistp256 need=32 dh_need=32
debug1: kex: ecdh-sha2-nistp256 need=32 dh_need=32
debug1: expecting SSH2_MSG_KEX_ECDH_REPLY
debug1: SSH2_MSG_KEX_ECDH_REPLY received
debug1: Server host key: ssh-rsa SHA256:5gSMQHqToW5REDACTEDt+vms
debug1: load_hostkeys: fopen /home/alex/.ssh/known_hosts2: No such file or directory
debug1: load_hostkeys: fopen /etc/ssh/ssh_known_hosts: No such file or directory
debug1: load_hostkeys: fopen /etc/ssh/ssh_known_hosts2: No such file or directory
debug1: Host 'apc-ups.barchem.de-eekhoorn.eu' is known and matches the RSA host key.
debug1: Found key in /home/alex/.ssh/known_hosts:54
ssh_dispatch_run_fatal: Connection to 172.17.255.240 port 22: error in libcrypto

My SSH Config:

### APC UPS ###
host apc-ups.my.net.work apc-ups 172.17.255.240
Hostname apc-ups.my.net.work
user apc
HostKeyAlgorithms +ssh-rsa
PubkeyAcceptedAlgorithms +ssh-rsa
PreferredAuthentications keyboard-interactive,password
KexAlgorithms +diffie-hellman-group1-sha1
Ciphers aes256-ctr
MACs hmac-sha2-256
PasswordAuthentication yes
PubkeyAuthentication no
VerifyHostKeyDNS no

#### DEFAULTS ####
Host *
LogLevel QUIET
ForwardAgent no
SendEnv LANG LC_*
HashKnownHosts no
Port 22
Protocol 2
ServerAliveInterval 15
ServerAliveCountMax 5
PubkeyAuthentication yes
PasswordAuthentication no
ChallengeResponseAuthentication no
ForwardX11 no
ForwardX11Trusted no
HostKeyAlgorithms ssh-ed25519-cert-v01@openssh.com,ssh-rsa-cert-v01@openssh.com,ssh-ed25519,ssh-rsa
Ciphers chacha20-poly1305@openssh.com,aes256-gcm@openssh.com,aes128-gcm@openssh.com,aes256-ctr,aes192-ctr,aes128-ctr
MACs hmac-sha2-512-etm@openssh.com,hmac-sha2-256-etm@openssh.com,umac-128-etm@openssh.com,hmac-sha2-512,hmac-sha2-256,umac-128@openssh.com
KexAlgorithms curve25519-sha256@libssh.org,diffie-hellman-group-exchange-sha256
VerifyHostKeyDNS yes

Client

"Fedora Linux 41 (Workstation Edition)"
6.12.10-200.fc41.x86_64 #1 SMP PREEMPT_DYNAMIC Fri Jan 17 18:05:24 UTC 2025 x86_64 GNU/Linux
openssh.x86_64 9.9p1-1.fc41 updates
openssl.x86_64 1:3.2.2-11.fc41 updates

NMC

* Model: AP9631 hw revision 5

* Application module: v7.1.8

* AOS v7.1.8

* Boot monitor v1.0.9

 

I don't really know what's wrong?

  • Tags:
  • english
  • ssh
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-17 06:41 AM

0 Likes
1
2573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-17 06:41 AM

Hello,

 

If you are using RedHat Linux or related distros ,you may have issues connecting to NMC's via SSH

 

Redhat has implemented changes to their crypto policies which can cause the SSH connection to fail with the following error message:
"ssh_dispatch_run_fatal: Connection to xxx.xxx.xxx.xxx port xx: error in libcrypto"

you can view the current policies by running the following command: "update-crypto-policies --show"
If the return output is "DEFAULT", you will need to enable legacy options.

This is done by running "update-crypto-policies --set LEGACY" with elevated privileges.

Once done, you will need to restart the linux machine in order for the policy changes to become active. 

 

Regards,

 

Karim

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-17 06:41 AM

0 Likes
1
2574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-17 06:41 AM

Hello,

 

If you are using RedHat Linux or related distros ,you may have issues connecting to NMC's via SSH

 

Redhat has implemented changes to their crypto policies which can cause the SSH connection to fail with the following error message:
"ssh_dispatch_run_fatal: Connection to xxx.xxx.xxx.xxx port xx: error in libcrypto"

you can view the current policies by running the following command: "update-crypto-policies --show"
If the return output is "DEFAULT", you will need to enable legacy options.

This is done by running "update-crypto-policies --set LEGACY" with elevated privileges.

Once done, you will need to restart the linux machine in order for the policy changes to become active. 

 

Regards,

 

Karim

Reply

Link copied. Please paste this link to share this article on your social media post.

aswen
aswen
Cadet

Posted: ‎2025-02-18 12:45 AM

In response to KarimEissa
0 Likes
0
2549
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-18 12:45 AM

Thanks @KarimEissa for showing me this work around. I'm using SSH to login to many systems and need to do that as secure as possible. Switching my entire SSH config back to LEGACY is, from that perspective, not the safest solution.
How can I configure the host entry of my APC card in `.ssh/config` so that I can login to the NMC without lowering the standards for all my connections? (I know that SSH tries to negotiate the securest option, but it's not without reason that some ciphers and kex algorithms are removed from DEFAULT).

Reply

Link copied. Please paste this link to share this article on your social media post.

KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-18 09:07 AM

0 Likes
0
2537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-18 09:07 AM

Hello,

 

You may need to refer to the below link for SSH connections to NMC 

 

https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/Scripting-SSH-connections-to-NMC-s-take-2...

 

 you may need to adjust the list of SSL/TLS ciphers in use for NMC web access on the NMC, to comply with local security policies, changes in browser compatibility, or to reflect ever-changing best practices.

 

Via the NMC command line:

Issue the “cipher” command to show the current enabled set, or “cipher help” for usage notes.
eg;

apc>cipher help
Usage: cipher --  Configuration Options
    Note: The minimal protocol setting is not considered when showing
           the available ciphers.

    cipher [-aes (enable | disable)] (AES)
           [-dh (enable | disable)] (DH)
           [-rsake (enable | disable)] (RSA Key Exchange)
           [-rsaau (enable | disable)] (RSA Authentication)
           [-sha1 (enable | disable)] (SHA)
           [-sha2 (enable | disable)] (SHA256)
           [-ecdhe (enable | disable)] (ECDHE)

Note:
Prior to 6.8.0, each option (eg -rc4) toggled the current state; these are now explicitly deterministic.
Reboot to commit changes.
 
Example:
List current settings, showing that all available are enabled (as default):
 

>cipher
E000: Success
Key Exchange Algorithms
-----------------------

        DH                   enabled
        RSA Key Exchange     enabled

Authentication Algorithms
-------------------------
(Warning: disabling the only algorithm in category
          will block all SSL/TLS sessions)

        RSA Authentication   enabled

Block Cipher Algorithms
-----------------------

        triple-DES           enabled
        RC4                  enabled
        AES                  enabled

MAC Algorithms
--------------

        MD5                  enabled
        SHA                  enabled
        SHA256               enabled

[...]
Disable RC4 cipher and RSA key-exchange:
 

>cipher -rc4 disable
E002: Success

>cipher -rsake disable
E002: Success


List new settings, confirming expected changes:
 

>cipher
E000: Success
Key Exchange Algorithms
-----------------------

        DH                   enabled
        RSA Key Exchange     disabled

Authentication Algorithms
-------------------------
(Warning: disabling the only algorithm in category
          will block all SSL/TLS sessions)

        RSA Authentication   enabled

Block Cipher Algorithms
-----------------------

        triple-DES           enabled
        RC4                  disabled
        AES                  enabled

MAC Algorithms
--------------

        MD5                  enabled
        SHA                  enabled
        SHA256               enabled

[...]

Using INI files (eg, for mass configuration):
 

[CryptographicAlgorithms]
;Warning: Changing these values can affect system access.
TripleDES=enabled
RC4=disabled
AES=enabled
DH=enabled
RSA_KE=disabled
RSA_Auth=enabled
MD5=enabled
SHA=enabled
SHA256=enabled


Using the web interface:

These settings are not yet exposed via the web UI.

Troubleshooting:

Be aware that disabling ciphers may affect browser compatibility; SSL/TLS will be unusable to the user unless their browser and the NMC have at least one cipher suite in common. Browser errors such as "ssl_error_no_cypher_overlap" or "err_ssl_version_or_cipher_mismatch" would indicate such an incompatibility.

 

Regards,

 

Karim

Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Commander Shaun Commander
Commander

Posted: ‎2025-02-19 05:28 AM . Last Modified: ‎2025-02-19 05:29 AM

0 Likes
0
2513
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-19 05:28 AM . Last Modified: ‎2025-02-19 05:29 AM

Hi @aswen,

 

This can't really be solved in the ssh config - this is the operating principle for Red Hat's crypto policies.  Your ssh configuration is correct, but when it attempts to use a routine that's disallowed by the current policy, libcrypto throws an exception.

 

This means we can't solve this on a per-host basis, the system-wide crypto policy is the blocker.

 

The least invasive configuration I've found to work is

 

 

update-crypto-policies --set DEFAULT:SHA1

 

 

Instead of setting the whole policy to LEGACY, this will leave us on DEFAULT except with sha1 re-enabled so the group1-sha1 kex is no longer a policy violation.  It is still a step down from DEFAULT, however - the only real alternative I've found to that is to have an alternate toolchain in a container, so the containerized ssh isn't using the host's libcrypto.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore