SRT6KRMXLT need to configure to accept 240V as input instead of the 208V it is set for now.
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-05-0205:24 AM
SRT6KRMXLT need to configure to accept 240V as input instead of the 208V it is set for now.
I have an SRT6KRMXLT that I am trying to feed with a generator that outputs 240V at 30 Amps. My SRT6KRMXLT is typically run from the building power and was set up for 208V as the input. But the generator only outputs 240V. Need to change the SRT6KRMXLT to use 240V for one day while we do some work on the power systems in the building. Thanks!
NOTE: Insure you fully understand the outputs need to be turned off before proceeding so schedule a maintenance window.
Validate the connected loads can operate on 240 VAC vs 208 VAC. Otherwise get ready to answer some hard questions about letting out the magic smoke! 🤣