Replacement battery for SMT1500C

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Replacement battery for SMT1500C
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
bohemianguitarguy
Ensign bohemianguitarguy
Ensign

Posted: ‎2022-11-13 12:59 PM . Last Modified: ‎2022-11-13 01:01 PM

1 Like
8
3392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-13 12:59 PM . Last Modified: ‎2022-11-13 01:01 PM

Replacement battery for SMT1500C

I have the SMT1500C UPS  that I purchased back in 2018. The battery has reached end of life and I need a replacement battery. I did some checking and wanted to confirm the best recommended replacement battery.

 

I found this battery replacement on Amazon.

 

I also found this battery replacement option, which was significantly less. Would that battery work in the unit I have? Would the battery life not be as long considering the price difference? I'm curious on the why the price difference is so much less.

 

I found another battery replacement that was a few dollars more than the option at Amazon.

 

When replacing the battery is it similar to doing a complete brain dead battery hard reset procedure? The reason I'm asking is because I have been dealing with the lost connection issues with my USB connection to the battery. I read that doing a complete brain dead hard reset fixes the lost connection issue in some circumstances. Hoping that might fix my lost connection issue after the battery is replaced.

 

I'd appreciate any feedback on the replacement battery for my unit.

  • Tags:
  • battery replacement
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-11-17 07:28 PM

0 Likes
7
3312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-17 07:28 PM

Hi @bohemianguitarguy 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.  Apologies for the inconvenience this has caused.  We recommend always using the APC Genuine Replacement Battery from authorized resellers/vendors.

 

Regarding your loss of communication issues, it is important that the UPS is running the latest firmware available.  You may refer to the FAQ article below for guidance.

 

How do I update the firmware of my CSH, SCL, SMC, SMT, SMTL, SMX, SRT, SRTL, XP, and XU series Smart... 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

bohemianguitarguy
Ensign bohemianguitarguy
Ensign

Posted: ‎2022-11-22 11:06 AM

In response to JonPro
0 Likes
6
3214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-22 11:06 AM

Hi @JonPro 

 


Thank you for your reply and the information you provided. I did get a replacement battery from an authorized vendor as you suggested. The battery is back up and running.

 

I logged into the apc smart connect dashboard and updated the firmware thru the smart connect dashboard interface. It now shows that the firmware is up-to-date. The release notes also indicates the lost connection issue being resolved in the firmware update.


However, I'm still encountering the lost connection thru the USB connection from my workstation to the the UPS. I have the APC SMT1500C Smart UPS with SmartConnect that I purchased back in 2018. I'm using a USB connection from my workstation to the USB connection on the UPS as my workstation does not have a serial port.

 

I can do a port reset by pressing the "enter" + "right arrow" keys simultaneously on the UPS and it reconnects the USB connection. The PowerChute Business Edition web interface status will go back online, but unfortunately the connection is dropped again after about 15 or 20 minutes. I have scoured the web looking for solutions and have tried a multitude of different solutions that have been suggested. I was hoping with the new battery it would be like a brain dead hard reset and potentially fix the issue.

 

The smart connect has remained connected and the dashboard notifications from smart connect have worked. It appears that only the USB connection is the problem. When I first purchased the UPS the USB connection worked seamlessly until about May of 2021 and then I started experiencing the lost connection. Any other possible suggestions on what I might try to fix this lost connection issue?

 

Regards

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-11-22 05:58 PM

In response to bohemianguitarguy
0 Likes
5
3207
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-22 05:58 PM

Hi,

 

Have you tried changing the USB cable and disabling the Green Mode functionality?  Kindly refer to the Operations Manual provided below on how to do that, it can be found on page 19.

 

Operation Smart-UPS SMT 750C/1000C/1500C/2200C/3000C VA 120/230 Vac Tower/RM2U 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

bohemianguitarguy
Ensign bohemianguitarguy
Ensign

Posted: ‎2022-11-23 10:45 AM

In response to JonPro
0 Likes
4
3197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-23 10:45 AM

Hi @JonPro 

 

Yes, I've actually tried multiple USB cables and trying to different USB ports and none solved the lost connection. I did try disabling "green" mode on the UPS and then did a port reset to re-establish the connection. The connection lasted about 20 minutes before losing the connection. Not sure what else to try.

 

I really do appreciate your help and the suggestions. If you know of anything else I should try, let me know. I'll keep digging and see if I can find a solution to the lost connection. It's probably something simple that I'm missing on my end 🙂

 

Thanks again!

Regards

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-11-23 04:19 PM

In response to bohemianguitarguy
0 Likes
3
3189
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-23 04:19 PM

@bohemianguitarguy 

 

What I could think of doing next is connecting the UPS to a different PC and installing PCBE on it.  By the way, what versions of PCBE and OS are you using?

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

bohemianguitarguy
Ensign bohemianguitarguy
Ensign

Posted: ‎2022-11-24 03:17 PM

In response to JonPro
0 Likes
2
3172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-24 03:17 PM

@JonPro 

 

I could potentially test the UPS on another PC by connecting it and installing PCBE on it. See if I still get the lost connection. I'll look into that and give that a try.

 

My OS is Windows 10 Pro

and the PCBE version is 10.0.5.301 it had been an earlier version until I upgraded to the latest version.

 

I could upgrade my OS to Windows 11, but I do like and prefer Windows 10 Pro because some of the changes to Windows 11 doesn't allow certain task bar features that I use with HWiNFO64 app like adding the task bar icons for the CPU and GPU temperature and the battery estimated runtime. If I upgrade to Windows 11 those features are no longer available.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

bohemianguitarguy
Ensign bohemianguitarguy
Ensign

Posted: ‎2022-11-26 01:04 PM

In response to bohemianguitarguy
0 Likes
1
3147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-26 01:04 PM

Hi @JonPro 

 

If I could run one more question by you. I've read a few different articles about the type of USB cable that is needed and also about the USB port being used that can cause issues. I saw this post about the USB port:

 

https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/Communication-Lost-in-a-Smart-UPS-1500-wi... 

 

When I purchased the UPS battery the USB cable was not included. I purchase the UPS from Amazon. Here is the unit I purchased:

 

https://www.amazon.com/gp/product/B0762QJ6Y1/ref=ppx_yo_dt_b_asin_title_o00_s00?ie=UTF8&psc=1

 

As I mentioned, I have tried several different USB cables and my workstation only has USB 2.0 and USB 3.0 ports. Do you know the correct USB cable I should be using for this unit? I'm wondering if I'm using the wrong USB cable. If there is an official USB cable that I need to get, do you have a link to that product? I'll try a new cable to see if it works.

 

Thanks!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-12-05 10:53 PM

In response to bohemianguitarguy
0 Likes
0
3031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-05 10:53 PM

Apologies for the delay in my response @bohemianguitarguy.

 

Yes, there are certain UPS that requires a special type of USB cable and upon checking the UPS that you have, it can use a regular USB A to A cable.

 

As far as I know, the USB cable should be directly connected to a USB port on the PC and not to a USB hub.  If possible, I suggest that you try removing other USB devices that you have connected to the PC and leave the UPS connected and observe.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore