Removing doors from Netshelter racks

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Removing doors from Netshelter racks
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-18 01:09 AM

0 Likes
3
1510
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-18 01:09 AM

Removing doors from Netshelter racks

We just installed some AR3140 and AR3350 racks in a new company data center - actually had APC come out and set them up since it's a new building and we don't have personnel onsite yet. For some reason, they installed them as closely as possible (side by side in rows of 6 racks per row) - using the little tiedown bars they connected them using the two closest holes, thus we can't figure out how to get the doors off very easily, especially the rear doors. But they have to come off somehow - the APC installers couldn't have tied the racks together with the doors on - once they tied them together they had to put the doors back on.

All the front doors open Left-Right, so we can remove the Front doors by removing the first one to the left and going right one cabinet at a time all the way across from there. But it's kinda dumb that you can't get the front door off rack 6 without removing the doors from 1-5 first. But the back doors being split (obviously) totally screws that option as you can only remove one single door on either end of the row... the doors inward from the row are all locked in. We can get them to 90-degrees open, and can raise them up off the hinge but that's about it.

I'd say just raising the feet and shimming each rack over to adjust to the better spacing would be easy, but APC also installed ladder rack between the rows and we've had cable installed using the ladders already. It's still an option as l don't think it will affect the cable lengths, but I'd certainly like to know if there is a trick we are missing removing these doors with the short gap between racks. Thanks.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-18 01:09 AM

0 Likes
0
1510
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-18 01:09 AM

I found an older install document that gives a little more insight. Seems like you explained it well, but I didn't quite get the picture until I found this... I cannot fully test it because I'm not in that data center right now, but in principal, it should work.

1094_pastedImage_3.png

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-18 01:09 AM

0 Likes
0
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-18 01:09 AM

Hello ahamilton,

The manual shows how to remove the doors before the enclosures are ganged. Once ganged the angle required to remove the door changes quite a bit. It's much shallower. To remove the doors once the enclosures are bayed please follow these directions:

1) Open the doors and unhook the ground wires, then shut the doors.

2) Begin to open one of the doors slowly and lift upwards while opening. The door should lift off of the hinges.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-18 01:09 AM

0 Likes
0
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-18 01:09 AM

Hello -

Sounds easy..!  I'll check it out and get back to you.

Thanks very much.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-18 01:09 AM

0 Likes
0
1511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-18 01:09 AM

I found an older install document that gives a little more insight. Seems like you explained it well, but I didn't quite get the picture until I found this... I cannot fully test it because I'm not in that data center right now, but in principal, it should work.

1094_pastedImage_3.png

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore