New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Powering healthcare digital imaging equipment
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-1409:01 AM
Powering healthcare digital imaging equipment
Hello
Does anybody has any experience with this equipment GVSUPS20K100B3H? can you share what type of equipment are you protecting? This UPS is designed to power loads with high peak currents and specially X-Ray generators, It includes a transformer. Have you seen any information on the principal of operation? how does the transformer helps supply the peak current?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-1306:22 AM
Hi Hector,
This UPS is a unique combination of 80 kVA UPS with a 20 kVA Input Transformer (480V In, 400V Out) to handle peak load current (350 Amps) in an optimized transformer design. Includes Input and Output disconnect on the bottom alongside the transformer.
Indeed the main application segment is the healthcare one mainly X-ray machines or other equipment with a permanent load below 20 kW but a high peak load (20-80 kW) for a few minutes.
The system load profiles for medical imaging systems are highly dependent on the area that is being scanned and how the body is scanned.
In the case of an X-ray, the system load profile might look like this:
Power Consumption X-Ray System
Mode
Average Power (KVA)
Peak Power (KVA)
Standby including movements
10 kVA
10
Standby including movements + Low-load Fluoroscopy
14
17
Standby including movements + Exposure
50 (~5 sec)
85 kVA
Also to answer your last question, Input transformers in UPS systems offer some inherent protection against voltage fluctuations and spikes by their design. Transformers have inductive reactance, which resists rapid changes in current. When a voltage spike or transient occurs, the transformer's inductive properties can limit the rate of voltage change, offering some mitigation against sudden voltage surges. However, it's important to note that while transformers provide certain levels of protection, they may not handle extreme voltage spikes or surges on their own. That's why in this case they're paired with a UPS that contains filtering, surge suppressing, voltage regulation, etc.
P.S. You might want to have a look at GVSOPT036 & GVSOPT037 which completes the healthcare solution.