PDU Failures and Life Span of PDU's

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PDU Failures and Life Span of PDU's
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

0 Likes
5
4666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

PDU Failures and Life Span of PDU's

Hello. What are the typical lifespans of Switched Rack and/or Basic Rack PDU's? Are error messages on the display indicative of needing to replace the PDU? My company wants to make sure that our PDU's can still allow power to pass through them even if the display indicates there is an error.

Is there a way to know the PDU will fail or does it just suddenly stop working?

Thank you.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • failure
  • lifespan
  • pdu
  • power
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

0 Likes
0
4665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

i believe we say PDUs typically have a 6 year lifespan. also, in addition to what terry mentioned, both metered and switch rack pdus have a primary and secondary power supply to help avoid any failures that would cause the relays to fail closed and turn off the output on the PDU. on a metered rack PDU, if there is an NMC failure/issue, the PDU will still pass power. on a switched rack PDU, usually if the NMC cannot boot or something else is wrong with it, the PDU will not output power due to the design and the relay boards, etc. not all competitors have a secondary power supply so if either fails, you still have a backup to avoid any dropped loads. the built in management card provides detailed alarms, logs, etc to help monitor the device and your load current at a minimum.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

0 Likes
0
4665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

If you access the PDU via the console or Telnet interface, the dual power supply status shows up in the device manager menu tree (Device Manager / Power Supply Status). I don't see it in the web interface on the PDU.

I believe Angela and I are both saying the same thing - that if the management card in the PDU fails, the loads will remain in their current state until input power is disconnected from the PDU. At that point, all outlets will be off and remain off until the management card successfully boots, any configured turn-on delays expire, and so on. If the management card doesn't boot for some reason, all outlets will remain off.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

0 Likes
0
4666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

yes, via the web UI you will only get a notification of when there is a fault with a power supply. in the telnet/ssh/local console, you can verify their status all of the time whether they are in a normal or fault state.

because a switched rack PDU offers outlet control and relays need to be open or closed to pass the power to the outlets, if the NMC and PDU cannot fully boot up, the PDU itself will not be able to operate the relays if there is an NMC hardware problem that prevents PDU booting. on a metered PDU it works differently due to the lack of individual outlet control so NMC fault or not, the PDU will still pass power.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

0 Likes
0
4666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

Speaking as a customer, I've had well over 100 units over the years, starting with the AP9210 (caution - well-known security issue) through to the current AP790x. I've never had one fail in a manner that dropped the load. The management board in these is actually separate from the piece that controls the power relays, communicating via a serial bus. Unless the management board sends a command in the correct format to the relay board, the relay board will ignore the management board.

That's for units which are powered on when the management board fails. The default state for the relays on the relay board is off, so if the management card doesn't tell them to turn on the load, unplugging the PDU from its power source and reconnecting it will not turn on the outlets if the management board isn't working.

The power path from the input plug to the outlets is pretty simple and I'd expect very few failures there. There seem to be redundant power supplies in the modern PDUs for powering the relays (the device status shows a primary and decondary power supply) so I wouldn't expect the relays to drop out from a power supply failure.

Aside from sudden catastrophic failure, the first thing you'll normally see are emails / log messages / traps (depending on what you configured) reporting warmstarts on the management card. This can indicate a developing hardware problem, or it can be a software problem. The newer units try to ping their default gateway and if it doesn't respond for 10 minutes or so, the management board decides it has a network problem and reboots to try to fix it. Some older software could also do a panic reboot when receiving malformed packets from an attacker. Later software corrected this. None of these things affect the loads plugged into the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

0 Likes
0
4666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

How do I determine if my PDU has a secondary power supply? I have a bunch of AP7941 PDU's, a few AP8941's, and a few AP7911A's. It doesn't seem to clearly indicate in the online documentation if they have secondary power supplies.

Angela states "on a switched rack PDU, usually if the NMC cannot boot or something else is wrong with it, the PDU will not output power due to the design and the relay boards" Being that a majority of our PDU's are switched rack PDU's does this mean that the PDU would not be able to pass power through it if the NMC has a problem hardware or software wise?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

0 Likes
0
4666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

i believe we say PDUs typically have a 6 year lifespan. also, in addition to what terry mentioned, both metered and switch rack pdus have a primary and secondary power supply to help avoid any failures that would cause the relays to fail closed and turn off the output on the PDU. on a metered rack PDU, if there is an NMC failure/issue, the PDU will still pass power. on a switched rack PDU, usually if the NMC cannot boot or something else is wrong with it, the PDU will not output power due to the design and the relay boards, etc. not all competitors have a secondary power supply so if either fails, you still have a backup to avoid any dropped loads. the built in management card provides detailed alarms, logs, etc to help monitor the device and your load current at a minimum.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

0 Likes
0
4666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

If you access the PDU via the console or Telnet interface, the dual power supply status shows up in the device manager menu tree (Device Manager / Power Supply Status). I don't see it in the web interface on the PDU.

I believe Angela and I are both saying the same thing - that if the management card in the PDU fails, the loads will remain in their current state until input power is disconnected from the PDU. At that point, all outlets will be off and remain off until the management card successfully boots, any configured turn-on delays expire, and so on. If the management card doesn't boot for some reason, all outlets will remain off.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

0 Likes
0
4667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:26 AM . Last Modified: ‎2024-03-18 01:31 AM

yes, via the web UI you will only get a notification of when there is a fault with a power supply. in the telnet/ssh/local console, you can verify their status all of the time whether they are in a normal or fault state.

because a switched rack PDU offers outlet control and relays need to be open or closed to pass the power to the outlets, if the NMC and PDU cannot fully boot up, the PDU itself will not be able to operate the relays if there is an NMC hardware problem that prevents PDU booting. on a metered PDU it works differently due to the lack of individual outlet control so NMC fault or not, the PDU will still pass power.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of