InRow RD Fluid Cooled

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • InRow RD Fluid Cooled
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:36 AM . Last Modified: ‎2024-03-18 04:20 AM

0 Likes
1
793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:36 AM . Last Modified: ‎2024-03-18 04:20 AM

InRow RD Fluid Cooled

Hi

I'm having a big time problems identifying all the components needed for Glykol based RD cooling.

Is there somewhere a detailed description of all components needed for RD InRow cooling (beside the RD unit and the outside Fluid Cooler)? I have been in touch with many cooling companies, but they are more interested in selling their own systems and they also claims they do not know the spesification for the items needed (and I understand that from what I can find of documents).

I'm very interested in only using RD cooling with Glycol and I hope someone could assist me. I have been in contact with APC in my own country, but they do not seem to know the details. There must be some more techincal details somewhere? If not, I have to go with my original though with simple aircondition.

I have seen the drawing in the InRow RD manual with different elements (glycol tank, pump etc), but they all seems small and no details on them. While the price on the outside unit (Fluid Cooler) and the InRow unit is manageable, I have recieved a price that is at least 6 to 8 times the costs of both these two compontents for the rest that is needed + work. So, I assume the pump, tank etc. on the inside is way more expensive than the rest?

Message was edited by: bareare

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:36 AM . Last Modified: ‎2024-03-18 04:19 AM

0 Likes
0
795
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:36 AM . Last Modified: ‎2024-03-18 04:19 AM

after doing a little research, we were able to come up with the following with a cooling expert at APC.

APC does not supply the pump(s) or expansion tank as standard equipment.*
The reason - these components are application specific. They have to be sized based on the entire glycol loop properties/specifications.*

For the pumps, one needs to make a decision as to the level of complexity and redundancy needed. The pump package can be as complex as a dual package with one pump in stand-by and one running, rotating them every few days, with alarms being send to a building management system, etc.*
Or, it can be as simple as a single pump, running at constant flow, all the time.*

When sizing the pumps, the flow has to be taken in consideration as well as the pressure drop.*
For the RD unit the flow required is 0.64 l/s.*
The pressure drop (or head) the pump has to be sized at, is the sum of all the pressure loss due to friction of the glycol circulating thru the loop. We publish the pressure drop in our equipment (RD and fluid cooler) in the technical manual. The pressure drop in the piping loop is a function of the length of the piping, the diameter, the material (steel, copper, etc), and all the other fittings, valves, elbows, etc.*

I don't want to make this seem more complicated than it is. This pressure drop information for different pipe sizes is available on the web or in engineering manuals.*

I think the best way is to have the same mechanical contractor or installation firm that install the piping, provide a pump package for this application. They should be able to calculate the size of the pumps based on the loop characteristics.*

I don't think the pump(s) should be more expensive than the fluid cooler or the RD unit.*

The same thing for the expansion tank. It is a very inexpensive piece of equipment. It is a small tank with a internal membrane that allow the fluid to expand and contract due to changes in temperature.*
The size of the expansion tank is determined based on the amount of glycol in the system.*
Again, any installing firm should be able to provide this tank without any problems.*

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:36 AM . Last Modified: ‎2024-03-18 04:19 AM

0 Likes
0
796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:36 AM . Last Modified: ‎2024-03-18 04:19 AM

after doing a little research, we were able to come up with the following with a cooling expert at APC.

APC does not supply the pump(s) or expansion tank as standard equipment.*
The reason - these components are application specific. They have to be sized based on the entire glycol loop properties/specifications.*

For the pumps, one needs to make a decision as to the level of complexity and redundancy needed. The pump package can be as complex as a dual package with one pump in stand-by and one running, rotating them every few days, with alarms being send to a building management system, etc.*
Or, it can be as simple as a single pump, running at constant flow, all the time.*

When sizing the pumps, the flow has to be taken in consideration as well as the pressure drop.*
For the RD unit the flow required is 0.64 l/s.*
The pressure drop (or head) the pump has to be sized at, is the sum of all the pressure loss due to friction of the glycol circulating thru the loop. We publish the pressure drop in our equipment (RD and fluid cooler) in the technical manual. The pressure drop in the piping loop is a function of the length of the piping, the diameter, the material (steel, copper, etc), and all the other fittings, valves, elbows, etc.*

I don't want to make this seem more complicated than it is. This pressure drop information for different pipe sizes is available on the web or in engineering manuals.*

I think the best way is to have the same mechanical contractor or installation firm that install the piping, provide a pump package for this application. They should be able to calculate the size of the pumps based on the loop characteristics.*

I don't think the pump(s) should be more expensive than the fluid cooler or the RD unit.*

The same thing for the expansion tank. It is a very inexpensive piece of equipment. It is a small tank with a internal membrane that allow the fluid to expand and contract due to changes in temperature.*
The size of the expansion tank is determined based on the amount of glycol in the system.*
Again, any installing firm should be able to provide this tank without any problems.*

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore