Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
How much power does the UPS SMT1500RMI1U consume when charging.
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-04-2204:15 PM
How much power does the UPS SMT1500RMI1U consume when charging.
Hello,
I am sizing a distribution transformer in a machine that uses the UPS SMT1500RMI1U as back up for the PC.
The UPS is rated 1500VA / 1000W, I am wondering if this is the power that will consume when charging of it is only the rated power available for the UPS load side?
Looking at the product datasheet I found the following specification:
Battery Charge Power (Watts)
73 W rated
Can I take this value as the charging power consumption? The battery model on this UPS is APCRBC88
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2025-04-2304:54 AM
The system you indicated can support 1000 watts RMS continuous. The 73 watt charger value is the maximum output it can provide to recharge a fully depleted battery cartridge.
The power output varies based on SOC, Temperature, and battery condition.
The SMT1500 has an idle power consumption of approximately 25 ~ 32 watts depending upon configuration and if green mode is enabled / disabled.