Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Galaxy 3:3 10 kVA software

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Galaxy 3:3 10 kVA software
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5059
voidstar_apc
voidstar_apc
196
Teken
Teken
162
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Uninterruptible Power Supply (UPS)

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Juwani_apc
Juwani_apc
Explorer

Posted: ‎2023-12-25 08:55 AM

0 Likes
5
3915
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-12-25 08:55 AM

Galaxy 3:3 10 kVA software

Hello everyone,

I hope this message finds you well. I'm in need of some assistance related to my Galaxy 300. Since the forum was migrated to the SE website, I lost access to the necessary software. Specifically, I require the latest firmware for the AP9631 card and the UPS tuner software to replace batteries in a 10-year-old UPS that's still functioning well.

I would greatly appreciate any help you could provide.

 

Thank you in advance.

 

Kind regards,
Sebastian

Labels
  • Labels:
  • Datacenter UPS
  • Tags:
  • english
  • software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Juwani_apc
Juwani_apc
Explorer

Posted: ‎2024-06-16 03:48 PM

0 Likes
0
3682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-16 03:48 PM

Up

Reply

Link copied. Please paste this link to share this article on your social media post.

MorneMeintjes
MorneMeintjes
Contributor

Posted: ‎2024-06-18 12:23 AM

0 Likes
2
3658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-18 12:23 AM

Good Morning.

Tuner is only for SE FSR's and their partner FSRs. If you have a way to obtain Tuner im listening. I believe that the battery alarm can be cleared using the NMC. I have not tried this method before. With your unit having a NMC you can try this method by dpierce4776

 

"Thant depends on which NMC you have and the firmware. If you have the 9640 or 9630. Then under UPS there is a spot for battery alarms timing. Put a -1 on both spots to clear the alarm"

 

Please let me know if this works, I have a unit 600km away that needs resetting. Going without a proven solution is not economical.

 

Let me know if it works.

Reply

Link copied. Please paste this link to share this article on your social media post.

MorneMeintjes
MorneMeintjes
Contributor

Posted: ‎2024-06-27 11:19 PM

In response to MorneMeintjes
0 Likes
1
3623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-27 11:19 PM

Good Morning

I had the opportunity to test the canceling of the Galaxy 300 via the NMC below.

 

"Thant depends on which NMC you have and the firmware. If you have the 9640 or 9630. Then under UPS there is a spot for battery alarms timing. Put a -1 on both spots to clear the alarm"

 

Unfortunately there is no option using the NMC to clear the battery alarm.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Juwani_apc
Juwani_apc
Explorer

Posted: ‎2024-06-28 10:57 PM

In response to MorneMeintjes
0 Likes
0
3597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-28 10:57 PM

Hi everyone,

I also can’t reset the alarm via NMC. It seems that the NMC functionality in the Galaxy 300 is quite limited. It lacks features such as:

• Changing output voltage
• Triggering a battery test
• Triggering a calibration test

I replaced the battery string myself, thoroughly checking each one for internal resistance and voltage. The battery string is working perfectly, but since I’m not a Schneider partner, I don’t have the software to adjust the charging current and clear the battery alarm. I’d be happy to establish such a partnership and would appreciate guidance on the official process.

If that’s not possible, could someone with the software assist remotely?

Thanks in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

Juwani_apc
Juwani_apc
Explorer

Posted: ‎2025-01-30 04:57 PM

0 Likes
0
3096
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-30 04:57 PM

Is there anyone here who can help me remotely?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore