Easy Micro Data Center (EMDC42UP1) UPS Swap

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Easy Micro Data Center (EMDC42UP1) UPS Swap
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
SJ_Datacom
Crewman SJ_Datacom
Crewman

Posted: โ€Ž2025-03-30 11:58 PM . Last Modified: โ€Ž2025-03-30 11:59 PM

0 Likes
5
215
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-03-30 11:58 PM . Last Modified: โ€Ž2025-03-30 11:59 PM

Easy Micro Data Center (EMDC42UP1) UPS Swap

We have a number of Easy Micro Data Centers that had to have the Easy-UPS (SRV240RLBP-9A) swapped out with a Smart-UPS (SRT6KRMXLI) primarily so that PowerChute software over the ethernet could be used for multiple devices within the MDC.

 

My issue is that since the swap out the MDC and it's front panel complain about loss of communication with the UPS. This is understandable given that the MDC "Monitor" connected to the Easy-UPS via RS232 (DB9) that the Smart-UPS physically does not have. The Smart-UPS does have a RJ45 port labelled as "Serial" on the rear but APC doesn't seem to sell an official RJ45 (Monitor connection) to RJ45 (UPS connection) cable.

Does anyone know of such a cable or some other solution?

Would daisy chaining a AP940-0625A cable to the one left behind from the Easy-UPS work or just cause more problems?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Teken
Spock Teken
Spock

Posted: โ€Ž2025-04-01 10:50 AM

0 Likes
4
195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-04-01 10:50 AM

For clarity sake the cable provided by APC is a RJ50 -> Serial. It is (NOT) a standard internally wired RJ45 Ethernet jack. 

 

Questions Ask . . . ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

SJ_Datacom
Crewman SJ_Datacom
Crewman

Posted: โ€Ž2025-04-01 08:46 PM

In response to Teken
0 Likes
3
170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-04-01 08:46 PM

I know what you're saying. It's very confusing however as a SRT6KRMXLI has NO documentation on the Serial port that's natively on the unit. It list NO cables as part numbers and the APC site shows nothing that's not RJ-45

Management Options and Cables | Schneider Electric New Zealand

Are these serial ports and cables gated to Schneider techs?

Reply

Link copied. Please paste this link to share this article on your social media post.

SJ_Datacom
Crewman SJ_Datacom
Crewman

Posted: โ€Ž2025-04-02 04:11 AM

In response to SJ_Datacom
0 Likes
1
158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-04-02 04:11 AM

Seems this might just be a marketing thing? The link I gave above clearly shows the cables as RJ-45. But this other forum thread seems to suggest that this is for marketing and the actual cable is in fact RJ-50.

Even the APC Smart-UPS Communications Application Note #181 clearly states that the SRT6KRMXLI is a RJ-45.

Smart-UPS Communications | Schneider Electric

 

We're going to source one of these AP940-0625A cables and I'll see if the Easy MDC will "support" the Smart-UPS and let people know here.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: โ€Ž2025-04-02 04:18 AM

In response to SJ_Datacom
0 Likes
0
167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-04-02 04:18 AM

You may use the Serial cable you referenced up above to communicate with the new system. 

Having said this Iโ€™m not clear as to what you want to do so any clarification would be great.

 

Finally, just to add some more clarity the system will only allow one serial connection at any one time.


Meaning you can not have both serial ports connected and operating in parallel without seeing negative results.

 

Questions Ask . . . ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: โ€Ž2025-04-02 08:12 AM

In response to SJ_Datacom
0 Likes
0
151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-04-02 08:12 AM

Just to be clear the NMC (Network Management Card) uses a standard RJ45 Ethernet port.

 

The Serial Port uses a RJ50 data port. There is another RJ45 port reserved for the universal I/O such as temperature, Temperature / Humidity, Dry Contacts etc.

 

Lastly, there is a Micro USB / USB-C for console access. The Remaining USB Ports are for Data and USB Flash Drive for firmware updates.

 

Questions Ask . . . ๐Ÿ‘ 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of