I am making a basic design for a high density data center, this room has 75 High Density Racks total. I am assuming a power comsumption of 10KW for each Rack and a requirement of 1388 CFM for each unit
the requirement comes from:
by APC white paper: 18kw ---->2500 CFM
so 10kw--->1388 CFM
75 units in the room x 1388=104100 CFM
so my flow requirement is more or less 104100 CFM for this computer room
I saw that I can configure a system based with 2 chillers of your brand, part number ACCH220N-ABA-D10S which is a Unit capable of a flow 49600 CFM. with two units I can cover my requirements.
so for this system I have two questions:
question 1: do I have anything wrong in my assumptions or numbers?
question 2:
I am trying to avoid Chillers because I dont want to put anything on the roof. what other alternatives do I have?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:48 PM . Last Modified: 2024-03-19 03:29 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:48 PM . Last Modified: 2024-03-19 03:29 AM
If the climate isn't cool enough you can't avoid chillers. Even if it's just a few weeks out of the year, that's a few weeks out of the year you'll have to take servers out of service for
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:48 PM . Last Modified: 2024-03-19 03:29 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-25 10:48 PM . Last Modified: 2024-03-19 03:29 AM
If the climate isn't cool enough you can't avoid chillers. Even if it's just a few weeks out of the year, that's a few weeks out of the year you'll have to take servers out of service for