APC 7723 remote switch source

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC 7723 remote switch source
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
magellano
Crewman magellano
Crewman

Posted: โ€Ž2022-11-23 08:14 AM

0 Likes
4
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-11-23 08:14 AM

APC 7723 remote switch source

Is it possible to switch source on an APC 7723 from a remote server executing command via ssh or snmp?

 

I'd like to swap source every x days. I can't find a schedule function on the web page...

 

Thanks

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Shaun
Commander Shaun Commander
Commander

Posted: โ€Ž2022-11-24 12:50 AM

In response to magellano
0 Likes
1
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-11-24 12:50 AM

Hi,

 

I think I was unclear - it's only the 'none' option that doesn't switch.  When a preferred source is set, it'll be used (as long as the input is acceptable).  I tested on a 7724 which should be "close enough" for this comparison, and the switch wasn't immediate, but it was less than 10 seconds.

 

So the options are: 

 

1: Prefers Source A, ATS will return to Source A when both inputs are acceptable.

2: Prefers Source B, ATS will return to Source B when both inputs are acceptable.

3: Has no preference, will remain on the current source as long as the current source is acceptable.

 

So I believe alternating between settings 1 & 2 will do what you need - I was just trying to expand on the "none" option as the one-word description is incredibly vague.

 

I can enter a feature request for source scheduler.  If you can share what real-world problem it solves, it helps prioritise such requests during development.  However, I should be clear that the 77xx isn't the current offer, so any improvements would almost certainly be made in the current series (AP44xxA). I'll also be honest that I'd expect this feature to be a relatively low priority - as every source-switch event has a non-zero risk, the platform leans towards being conservative in its switching.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Shaun
Commander Shaun Commander
Commander

Posted: โ€Ž2022-11-23 08:33 AM

0 Likes
3
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-11-23 08:33 AM

Hi @magellano,

 

There is an OID you can write to:

 

.1.3.6.1.4.1.318.1.1.8.4.2.0   - PowerNet-MIB::atsConfigPreferredSource.0
SYNTAX INTEGER {sourceA(1), sourceB(2), none(3)}
DESCRIPTION "This variable returns the preferred source of power when both sources are OK."

 

So if you write 1 to this it'll prefer source A, 2 for source B, and 3 will have no preference (it'll only switch when given a reason to switch, rather than switching to re-establish a preferred source).

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

magellano
Crewman magellano
Crewman

Posted: โ€Ž2022-11-23 11:44 PM

In response to Shaun
0 Likes
2
1369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-11-23 11:44 PM

From what you wrote, I can change the preferred source but the ATS will not change until an event that will force to switch.

Is it right?

So it doesn't work for my needs: I would like to switch the used source on a scheduled time.

Is it possible?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Commander Shaun Commander
Commander

Posted: โ€Ž2022-11-24 12:50 AM

In response to magellano
0 Likes
1
1364
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-11-24 12:50 AM

Hi,

 

I think I was unclear - it's only the 'none' option that doesn't switch.  When a preferred source is set, it'll be used (as long as the input is acceptable).  I tested on a 7724 which should be "close enough" for this comparison, and the switch wasn't immediate, but it was less than 10 seconds.

 

So the options are: 

 

1: Prefers Source A, ATS will return to Source A when both inputs are acceptable.

2: Prefers Source B, ATS will return to Source B when both inputs are acceptable.

3: Has no preference, will remain on the current source as long as the current source is acceptable.

 

So I believe alternating between settings 1 & 2 will do what you need - I was just trying to expand on the "none" option as the one-word description is incredibly vague.

 

I can enter a feature request for source scheduler.  If you can share what real-world problem it solves, it helps prioritise such requests during development.  However, I should be clear that the 77xx isn't the current offer, so any improvements would almost certainly be made in the current series (AP44xxA). I'll also be honest that I'd expect this feature to be a relatively low priority - as every source-switch event has a non-zero risk, the platform leans towards being conservative in its switching.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

magellano
Crewman magellano
Crewman

Posted: โ€Ž2022-11-24 02:46 AM

In response to Shaun
0 Likes
0
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2022-11-24 02:46 AM

Thank you very much.

Just found that Network Ups Tools -NUT- (I have already installed it) can interact with ATS units.

 

So I must found the way to use it. ๐Ÿ™‚ 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore