hello,
any OIDs for AP8XXX series rack PDUs will be located under:
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2 / .1.3.6.1.4.1.318.1.1.26
for kW and max kW, try:
The power consumption of the Rack PDU load in hundredths of kiloWatts
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2.rPDU2Device.rPDU2DeviceStatusTable.rPDU2DeviceStatusEntry.rPDU2DeviceStatusPower
.1.3.6.1.4.1.318.1.1.26.4.3.1.5
The peak power consumption of the Rack PDU load in hundredths of kiloWatts
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2.rPDU2Device.rPDU2DeviceStatusTable.rPDU2DeviceStatusEntry.rPDU2DeviceStatusPeakPower
.1.3.6.1.4.1.318.1.1.26.4.3.1.6
You can also get the time stamp when the peak value occurred:
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2.rPDU2Device.rPDU2DeviceStatusTable.rPDU2DeviceStatusEntry.rPDU2DeviceStatusPeakPowerTimestamp
.1.3.6.1.4.1.318.1.1.26.4.3.1.7
hope that helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:26 AM . Last Modified: 2024-03-18 01:32 AM
hello,
any OIDs for AP8XXX series rack PDUs will be located under:
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2 / .1.3.6.1.4.1.318.1.1.26
for kW and max kW, try:
The power consumption of the Rack PDU load in hundredths of kiloWatts
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2.rPDU2Device.rPDU2DeviceStatusTable.rPDU2DeviceStatusEntry.rPDU2DeviceStatusPower
.1.3.6.1.4.1.318.1.1.26.4.3.1.5
The peak power consumption of the Rack PDU load in hundredths of kiloWatts
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2.rPDU2Device.rPDU2DeviceStatusTable.rPDU2DeviceStatusEntry.rPDU2DeviceStatusPeakPower
.1.3.6.1.4.1.318.1.1.26.4.3.1.6
You can also get the time stamp when the peak value occurred:
.iso.org.dod.internet.private.enterprises.apc.products.hardware.rPDU2.rPDU2Device.rPDU2DeviceStatusTable.rPDU2DeviceStatusEntry.rPDU2DeviceStatusPeakPowerTimestamp
.1.3.6.1.4.1.318.1.1.26.4.3.1.7
hope that helps.