7721 Communication has been lost to device and leds flashing always from left to right

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 7721 Communication has been lost to device and leds flashing always from left to right
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 12:13 AM . Last Modified: β€Ž2024-03-18 11:34 PM

0 Likes
2
1028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 12:13 AM . Last Modified: β€Ž2024-03-18 11:34 PM

7721 Communication has been lost to device and leds flashing always from left to right

Hi

I need help!

Sorry for my english.

A have a problem after upgrade firmware - Communication has been lost to device and leds flashing always from left to right.

During the firmware update on the indicator was lights do - co - er.

Reset has not helped.

After hardreset Source A is not works.

 

It was before upgrade

After

result of fw_upgrade_r2.exe

Starting Upgrade 02/16/17: 16:00:41    
-----------------
02/16/17: 16:00:41   xxx.xxx.97.84: Testing device connection
02/16/17: 16:00:41   xxx.xxx.97.84: Device connection passed
02/16/17: 16:00:42   xxx.xxx.97.84: Testing FTP Log-in
02/16/17: 16:00:45   xxx.xxx.97.84: FTP Log-in passed
02/16/17: 16:00:46   xxx.xxx.97.84: Saving data file
02/16/17: 16:01:01   xxx.xxx.97.84: AOS Prior to firmware transfer: Network Management Card AOS v3.5.7
02/16/17: 16:01:01   xxx.xxx.97.84: APP Prior to firmware transfer: Automatic Transfer Switch APP v3.5.6
02/16/17: 16:01:21   xxx.xxx.97.84: Saving event & configuration files
02/16/17: 16:01:31   xxx.xxx.97.84: Transferring OS
02/16/17: 16:01:57   xxx.xxx.97.84: OS transfer successful
02/16/17: 16:01:59   xxx.xxx.97.84: Rebooting device
02/16/17: 16:02:19   xxx.xxx.97.84: Testing device connection
02/16/17: 16:02:53   xxx.xxx.97.84: Device connection passed
02/16/17: 16:02:54   xxx.xxx.97.84: Testing FTP Log-in
02/16/17: 16:02:55   xxx.xxx.97.84: FTP Log-in successful
02/16/17: 16:02:56   xxx.xxx.97.84: Transferring application
02/16/17: 16:03:28   xxx.xxx.97.84: Rebooting device
02/16/17: 16:03:38   xxx.xxx.97.84: Testing device connection
02/16/17: 16:04:10   xxx.xxx.97.84: AOS Post firmware transfer: Network Management Card AOS v3.9.2
02/16/17: 16:04:10   xxx.xxx.97.84: APP Post firmware transfer: Automatic Transfer Switch APP v3.9.2
02/16/17: 16:04:20   xxx.xxx.97.84: OS & Application transfer completed

events.log

02/17/2017     10:57:46     Automatic Transfer Switch: 7-Segment display hardware initialized.
02/17/2017     10:57:46     Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
02/17/2017     10:57:25     System: Coldstart.
02/17/2017     07:55:08     System: Configuration change. BOOTP server address.
02/17/2017     07:55:08     System: Configuration change. DHCP lease time.
02/17/2017     07:55:08     System: Configuration change. DHCP lease date.
02/17/2017     07:49:57     Automatic Transfer Switch: 7-Segment display hardware initialized.
02/17/2017     07:49:57     Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
02/17/2017     07:49:37     System: Coldstart.
02/16/2017     17:11:14     Automatic Transfer Switch: 7-Segment display hardware initialized.
02/16/2017     17:11:14     Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
02/16/2017     17:11:03     System: Network service started. System IP is xxx.xxx.97.84 from current DHCP lease.
02/16/2017     17:11:03     System: Warmstart.
02/16/2017     17:06:00     Automatic Transfer Switch: 7-Segment display hardware initialized.
02/16/2017     17:06:00     Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
02/16/2017     17:05:49     System: Network service started. System IP is xxx.xxx.97.84 from current DHCP lease.
02/16/2017     17:05:49     System: Warmstart.
02/16/2017     17:04:41     System: Initializing data in the Email file.
02/16/2017     17:04:41     System: Initializing data in the HTTP file.
02/16/2017     17:04:41     System: Initializing data in the Modem file.
02/16/2017     17:04:41     System: Initializing data in the RADIUS file.
02/16/2017     17:04:41     System: Initializing data in the DNS file.
02/16/2017     17:04:41     System: Configuration change. Secondary DNS server address.
02/16/2017     17:04:41     System: Configuration change. Primary DNS server address.
02/16/2017     17:04:41     System: Configuration change. NTP disabled.
02/16/2017     17:04:41     System: Configuration change. NTP GMT offset.
02/16/2017     17:04:41     System: Configuration change. Primary NTP server address.
02/16/2017     17:04:41     System: Initializing data in the NTP file.
02/16/2017     17:04:38     System: Initializing data in the Diagnostic file.
02/16/2017     17:04:38     System: Initializing data in the File Transfer file.
02/16/2017     17:04:38     System: Initializing data in the TFTP Client file.
02/16/2017     17:04:38     System: Configuration change. System administrator password.
02/16/2017     17:04:38     System: Configuration change. System location.
02/16/2017     17:04:38     System: Configuration change. System name.
02/16/2017     17:04:38     System: Configuration change. System contact.
02/16/2017     17:04:38     System: Initializing data in the System file.
02/16/2017     17:04:38     System: Initializing data in the FTP Client file.
02/16/2017     17:04:38     System: Initializing data in the FTP Server file.
02/16/2017     17:04:38     System: Initializing data in the Telnet file.
02/16/2017     17:04:38     System: Configuration change. Domain name.
02/16/2017     17:04:38     System: Configuration change. Host name.
02/16/2017     17:04:38     System: Initializing data in the Advanced TCP/IP file.
02/16/2017     17:04:37     System: Reset to Defaults by user apc.
02/16/2017     17:01:18     System: Console user 'apc' logged out from serial port.
02/16/2017     16:53:17     Automatic Transfer Switch: 7-Segment display hardware initialized.
02/16/2017     16:53:17     Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
02/16/2017     16:53:06     System: Network service started. System IP is xxx.xxx.97.84 from current DHCP lease.
02/16/2017     16:53:06     System: Warmstart.
02/16/2017     16:52:46     System: Restarting. Console user request.
02/16/2017     16:25:25     Automatic Transfer Switch: 7-Segment display hardware initialized.
02/16/2017     16:25:25     Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
02/16/2017     16:25:17     System: FTP user 'apc' logged in from xxx.xxx.97.30.
02/16/2017     16:25:13     System: Network service started. System IP is xxx.xxx.97.84 from current DHCP lease.
02/16/2017     16:25:13     System: Warmstart.
02/16/2017     16:17:59     Automatic Transfer Switch: 7-Segment display hardware initialized.
02/16/2017     16:17:59     Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
02/16/2017     16:17:48     System: Network service started. System IP is xxx.xxx.97.84 from current DHCP lease.
02/16/2017     16:17:48     System: Warmstart.
02/16/2017     16:17:29     System: Restarting. Web user request.
02/16/2017     16:04:39     Automatic Transfer Switch: ATS Lost communication.
02/16/2017     16:04:21     Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.
02/16/2017     16:04:21     Automatic Transfer Switch: ATS Communication established.
02/16/2017     16:04:07     Automatic Transfer Switch: ATS Controller firmware download failed.
02/16/2017     16:03:54     Automatic Transfer Switch: ATS Controller firmware download begun.
02/16/2017     16:03:49     System: FTP user 'apc' logged out from xxx.xxx.97.30.
02/16/2017     16:03:48     Automatic Transfer Switch: 7-Segment display hardware initialized.
02/16/2017     16:03:48     Automatic Transfer Switch: Phase Leds/Push-button hardware initialized.
02/16/2017     16:03:34     System: FTP user 'apc' logged in from xxx.xxx.97.30.
02/16/2017     16:03:27     System: Network service started. System IP is xxx.xxx.97.84 from current DHCP lease.
02/16/2017     16:03:27     System: Warmstart.
02/16/2017     16:00:25     System: FTP user 'apc' logged in from xxx.xxx.97.30.
02/16/2017     15:58:00     System: Web user 'apc' logged in from xxx.xxx.97.30.
02/16/2017     15:56:14     Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 12:13 AM . Last Modified: β€Ž2024-03-18 11:34 PM

0 Likes
0
1028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 12:13 AM . Last Modified: β€Ž2024-03-18 11:34 PM

I learned what does not work baseboard
Management card works on a different device
but the main board does not work on another ATS

So, if you do the update correctly, you have a chance to kill the device 😞

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 12:13 AM . Last Modified: β€Ž2024-03-18 11:34 PM

0 Likes
0
1028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 12:13 AM . Last Modified: β€Ž2024-03-18 11:34 PM

I did everything right during upgrade.
The second input is still not connected.
I tried to reset, switch off for a few hours, but Input A is not working, the ATS App does not load.

What other ideas or actions I can try?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 12:13 AM . Last Modified: β€Ž2024-03-18 11:34 PM

0 Likes
0
1029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 12:13 AM . Last Modified: β€Ž2024-03-18 11:34 PM

I learned what does not work baseboard
Management card works on a different device
but the main board does not work on another ATS

So, if you do the update correctly, you have a chance to kill the device 😞

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore