2N Power Distribution - STS still required if using dual cord loads?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 2N Power Distribution - STS still required if using dual cord loads?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
karbonphiber_apc
Lieutenant JG karbonphiber_apc
Lieutenant JG

Posted: โ€Ž2021-06-25 10:48 PM . Last Modified: โ€Ž2024-03-19 03:28 AM

0 Likes
4
1869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 10:48 PM . Last Modified: โ€Ž2024-03-19 03:28 AM

2N Power Distribution - STS still required if using dual cord loads?

For single cord loads I can see the need for an STS. However, for dual cord loads my thought is that switching between power sources can be performed right at the load level. I have someone else telling me that this is not as reliable...

Opinions welcome.

Labels
  • Labels:
  • Server Room & Data Center Design Best Practices
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-25 10:48 PM . Last Modified: โ€Ž2024-03-19 03:28 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 10:48 PM . Last Modified: โ€Ž2024-03-19 03:28 AM

It depends on what TIER level you want to have in your DC. If you want a TIER 4 you need an STS at every level of your power distribution.

We use 2n UPS connected to STS, connected to RPP PDUs, connected to rack ATS for single cord loads.

Dual cord loads are connected to 2 rack PDUs which are connected to different RPPs, so there's always an ATS/STS between a power cord and the UPSs.

Our DC is TIER 3.

What you could encounter, if you have a high load server connected to 2 PDUs and no ATSs is, that one PSU can't take the whole load and breaks in case of a power path failing. Maybe because it had a defect which didn't come to light because it ran at > 50% load all the time. I have seen that in our DC.

I guess that is what the person meant who talked to you.

I don't agree with mihail on the direct connection to the utility. You should always connect devices to UPSs. They will filter the current and your devices will live longer.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-25 10:48 PM . Last Modified: โ€Ž2024-03-19 03:28 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 10:48 PM . Last Modified: โ€Ž2024-03-19 03:28 AM

I can see two sides to this discussion.
The points provided above are based on all the loads having dual power supplies (redundant power supplies) and that they all work. However, all these redundant power supplies become single points of failure if one or the other electrical service is down for either service or mishap.

Placing a single STS between the main electrical services does indeed add another device to the system. It also reduces the risk of downtime due to single source loads and/or failed redundant power supplies.

Placing STS at the load, either at Rack level or at individual load level (or by inherent redundancy) adds many devices to the system and places many more single points of failure in the system.

In either case, I believe adding STS is going to raise the availability of the system regardless of where it's placed. I would prefer a single STS at the sources.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-25 10:48 PM . Last Modified: โ€Ž2024-03-19 03:28 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 10:48 PM . Last Modified: โ€Ž2024-03-19 03:28 AM

Hi there,

always keep in mind that, the set-up has to be as simple as possible. less components in, more reliable. more equipments, more points of failure, more downtime if trouble. also, easier to identify the trouble if any.
My opinion: if you have dual power supply loads, keep one side directly on the UPS, and the 2nd directly on Normal AC Source. you choose which is where to be tie.
so, actually the STS function is already present in your dual power supply load. ๐Ÿ˜‰

take care.

Mihail

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-25 10:48 PM . Last Modified: โ€Ž2024-03-19 03:28 AM

0 Likes
0
1866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 10:48 PM . Last Modified: โ€Ž2024-03-19 03:28 AM

i agree with the above post. with dual corded power supplies, i don't think you need an STS since it will be done at the load level as you mentioned. and to echo the above poster, the more pieces of equipment introduced, the more points of failure.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-25 10:48 PM . Last Modified: โ€Ž2024-03-19 03:28 AM

0 Likes
0
1867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-25 10:48 PM . Last Modified: โ€Ž2024-03-19 03:28 AM

It depends on what TIER level you want to have in your DC. If you want a TIER 4 you need an STS at every level of your power distribution.

We use 2n UPS connected to STS, connected to RPP PDUs, connected to rack ATS for single cord loads.

Dual cord loads are connected to 2 rack PDUs which are connected to different RPPs, so there's always an ATS/STS between a power cord and the UPSs.

Our DC is TIER 3.

What you could encounter, if you have a high load server connected to 2 PDUs and no ATSs is, that one PSU can't take the whole load and breaks in case of a power path failing. Maybe because it had a defect which didn't come to light because it ran at > 50% load all the time. I have seen that in our DC.

I guess that is what the person meant who talked to you.

I don't agree with mihail on the direct connection to the utility. You should always connect devices to UPSs. They will filter the current and your devices will live longer.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of