You'll need a 32 bit unsigned int and use a script program to combine the two 16 bit values you need for registers 4104 & 4105 into a 32 bit value, then bind the script output of the 32 bit value to a Modbus analogue output point set as 32 bit unsigned int, when it writes it should use FC16 so both will be writen together. But be aware at release 3.2.x there were issues with only writing on the first occasion.