Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84322members
353480posts

RemoteConnect

Remote Operations Forum

Collaborate and share knowledge on the extensive range of remote systems and devices, including SCADA radios and RTUs, on the Schneider Electric Exchange Remote Operations (formerly SCADA & Telemetry) forum. From commissioning SCADA integration devices and software, to enhancing existing installations or troubleshooting, connect with a global community of experts and users. Subscribe today.

BBEST
Crewman
Crewman
0 Likes
2
620

RemoteConnect

How do you assign a direct Modbus address to an object in RemoteConnect

2 Replies 2
AlastairF
Lieutenant Lieutenant
Lieutenant
0 Likes
0
617

Re: RemoteConnect

This is detailed in the Help.  Have a look at:
Navigation: SCADAPack x70 Configuration > Configuring SCADAPack x70 Device Operation > Configuring Database Objects > Adding Objects

and also:

Navigation: SCADAPack x70 Configuration > Configuring SCADAPack x70 Device Operation > Configuring Database Objects > Configuring Parameter Settings Using the Object Editor > Modbus Tab

In this section, the descriptor is for objects with register addresses. If you are dealing with Discrete objects then the choice is 1..9999 (Read/ write Discrete Coils) and 10001..19999 (Discrete Inputs)

Joel_Weder
Commander Commander
Commander
0 Likes
0
611

Re: RemoteConnect

There are quite a few Youtube videos on the Schneider Electric channel, discussing both basic and advanced aspects of RemoteConnect. Last year I created a series of five videos which provided a basic introduction, then showed such things as how to configure objects. Here's a link to the series of videos:

 

https://www.youtube.com/watch?v=EVwk7ADhCqE&t

https://www.youtube.com/watch?v=9D39x68AoFk&t

https://www.youtube.com/watch?v=B_-HFOVPJrA&t     <+==

https://www.youtube.com/watch?v=rPo1OOSy3TI&t

https://www.youtube.com/watch?v=xHBoVzc16_E&t

 

These videos unfortunately don't show actually configuring a Modbus point, but between about 3:40 and 4:30 in video #3 it shows where this can be done. Once you're there, the process is simple. By the way, you can configure an object with both a Modbus AND a DNP3 address if desired!

 

Joel Weder
Remote Operations Specialist
Schneider Electric