Reading RTU configurations clearSCADA

Remote Operations Forum

Collaborate and share knowledge on the extensive range of remote systems and devices, including SCADA radios and RTUs, on the Schneider Electric Exchange Remote Operations (formerly SCADA & Telemetry) forum. From commissioning SCADA integration devices and software, to enhancing existing installations or troubleshooting, connect with a global community of experts and users. Subscribe today.

Solved
RichardThiago
Cadet
0 Likes
4
1756

Reading RTU configurations clearSCADA

Message imported from previous forum - Category:SCADAPack RTU<<
User: ROVSCADAENGINEER, originally posted: 2019-06-19 01:59:38 Id:452
is it possible to read RTU configurations from sites from RTU's in clear SCADA.

I know you can do this with SCADAPack E-Configurator tool.

But can you do this in clearSCADA so that the process can be automated.

Thanks in advance.


Accepted Solutions
RW_Support
Ensign Ensign
Ensign
0 Likes
3
1744

Re: Reading RTU configurations clearSCADA

Hello,

 

The feature to read a RTU configuration and logic from ClearSCADA / Geo SCADA is not possible. ClearSCADA is able to monitor and configure the SCADAPack E remote assets via download or partial download of configuration (and logic) only.

See Answer In Context

4 Replies 4
RW_Support
Ensign Ensign
Ensign
0 Likes
3
1745

Re: Reading RTU configurations clearSCADA

Hello,

 

The feature to read a RTU configuration and logic from ClearSCADA / Geo SCADA is not possible. ClearSCADA is able to monitor and configure the SCADAPack E remote assets via download or partial download of configuration (and logic) only.

BevanWeiss
Spock
Spock
0 Likes
1
1609

Re: Reading RTU configurations clearSCADA

@RW_Support  I think your answer here is a little too concise.

It is absolutely possible to 'read' the E-series RTU configuration from a DNP3 connected RTU into ClearSCADA.

This is exactly what the 'Upload Configuration' option does.  What is not possible with the E-series RTUs is for this action to also reconfigure ClearSCADA.  It will only upload the .RTU file (or another file, which might be the ISaGRAF application).

 

You would need to manually align the two there after.  For the logic, you could just attach the ISaGRAF application back into the RTU Configuration, and it would be downloaded along with the configuration next time.

You could arguably do the same for the .RTU configuration file also, but you shouldn't use the 'Generate' option out of ClearSCADA for the Outstation then...


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
bansalrehana
Crewman
Crewman
0 Likes
0
1245

Re: Reading RTU configurations clearSCADA