Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84571members
353844posts

[Imported] Modbus Values from Generator

Remote Operations Forum

Collaborate and share knowledge on the extensive range of remote systems and devices, including SCADA radios and RTUs, on the Schneider Electric Exchange Remote Operations (formerly SCADA & Telemetry) forum. From commissioning SCADA integration devices and software, to enhancing existing installations or troubleshooting, connect with a global community of experts and users. Subscribe today.

sbeadle
Janeway Janeway
Janeway
0 Likes
0
422

[Imported] Modbus Values from Generator

>>Message imported from previous forum - Category:SCADAPack RTU<<
User: mchartrand, originally posted: 2018-10-25 14:50:30 Id:216
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

_______

**_zimmer:
I am having a specific problem getting the fuel level from a decision maker 3000 generator controller. Using modscan directly connected to the generator via laptop I can get the value from register 417000 as stated in the manual for the analog input associated with the fuel level, but I cannot figure out how to use the MSIP command to get this register. Will I have to re-map it somehow to a register that the scadapack 334 can read?
Thanks_**

__________________

bevanweiss:

If you're using ISaGRAF, then an IO Board should do the job.
Whether your SCADApack supports ISaGRAF is unknown, you didn't say what SCADApack.

Whether Modbus RTU / TCP is unknown, you didn't say which.

The Modbus address you've typed is a 6-digit address, the older ISaGRAF v3 may not have supported this (I can't remember). ISaGRAF v5 (SCADApack Workbench 6) does for E-series SCADApacks.

_____________________

a062549:
I have several of the older 3000's and I take the 40039 register (Fuel Rate* (RO WORD) /Gallons/Hour x 100 (ECM only)) and run it with a clock to figure the fuel burn and resultant fuel left scenario?