Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84705members
354089posts

[Imported] Configure 10 minutes interval report in RealFlo

Remote Operations Forum

Collaborate and share knowledge on the extensive range of remote systems and devices, including SCADA radios and RTUs, on the Schneider Electric Exchange Remote Operations (formerly SCADA & Telemetry) forum. From commissioning SCADA integration devices and software, to enhancing existing installations or troubleshooting, connect with a global community of experts and users. Subscribe today.

sbeadle
Janeway Janeway
Janeway
0 Likes
0
317

[Imported] Configure 10 minutes interval report in RealFlo

>>Message imported from previous forum - Category:Realflo Electronic Flow Measurement<<
User: mchartrand, originally posted: 2018-10-17 18:23:02 Id:68
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

-------------------------------

**_riane:
We have a RealFlo 6 on ScadaPack32, as we know that we can get the hourly and daily reports from RealFlo.
We need to read the accumulate flow of 10 minutes intervals. Pleas, is there any way to configure, and then get the 10 minutes interval report_**

________________

du5tin:
We generally use a TELEPACE program that contains a DLOG block in conjunction with RealFlo to get better logging resolution. Using this method you can DLOG the data points every ten minutes (or more often if you want) and pull out the logs with ClearSCADA or the SCADALog software.
Haven't built this in ISAGRAF but its likely easily done there as well.
For one client they log the tubing and casing pressure in the same DLOG so the production data all goes together.