[Imported] 4102 / 4203 tap location

Remote Operations Forum

Collaborate and share knowledge on the extensive range of remote systems and devices, including SCADA radios and RTUs, on the Schneider Electric Exchange Remote Operations (formerly SCADA & Telemetry) forum. From commissioning SCADA integration devices and software, to enhancing existing installations or troubleshooting, connect with a global community of experts and users. Subscribe today.

sbeadle
Janeway Janeway
Janeway
0 Likes
0
467

[Imported] 4102 / 4203 tap location

>>Message imported from previous forum - Category:Realflo Electronic Flow Measurement<<
User: mchartrand, originally posted: 2018-10-17 18:55:26 Id:85
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

-------------------------------

**_dirtydodge:
Does anyone know if the 4102 and 4203 transmitters use an "Upstream" or "Downstream" tap location for the static pressure?_**

____________________________________

mchartrand:
Hello,
They can be used for either location. The location is set in the configuration of the RealFLO flow run.