GP10 Field Unit showing "2049"

Remote Operations Forum

Collaborate and share knowledge on the extensive range of remote systems and devices, including SCADA radios and RTUs, on the Schneider Electric Exchange Remote Operations (formerly SCADA & Telemetry) forum. From commissioning SCADA integration devices and software, to enhancing existing installations or troubleshooting, connect with a global community of experts and users. Subscribe today.

Solved
jen6190
Ensign Ensign
Ensign
0 Likes
3
1881

GP10 Field Unit showing "2049"

My field units GP10 are showing "2049" as device status instead of showing 1 or 0, i have tried resetting the field units several times.


Accepted Solutions
Hardin4019
Lieutenant
Lieutenant
0 Likes
2
1869

Re: GP10 Field Unit showing "2049"

The device status of Accutechs can be added together. You are getting a 1 + 2048. If memory serves correctly, 2048 is a code indicating that the configuration of the device was changed through the buttons on the unit. It's not a bad thing, just informational. More details can be found in the free Accutech Manager software's help files.

See Answer In Context

3 Replies 3
Hardin4019
Lieutenant
Lieutenant
0 Likes
2
1870

Re: GP10 Field Unit showing "2049"

The device status of Accutechs can be added together. You are getting a 1 + 2048. If memory serves correctly, 2048 is a code indicating that the configuration of the device was changed through the buttons on the unit. It's not a bad thing, just informational. More details can be found in the free Accutech Manager software's help files.

jen6190
Ensign Ensign
Ensign
0 Likes
1
1867

Re: GP10 Field Unit showing "2049"

But in my E configurator, it shows Engineering unit exceeded when reading the DNP3 point, do i adjust the engineering unit to accomodate this value or is there a way that i can split this to get my 1 seperate from the 2048?

Hardin4019
Lieutenant
Lieutenant
0 Likes
0
1856

Re: GP10 Field Unit showing "2049"

Yes. You will have to lookup what the maximum range of the value could be from the Accutech Manager software help file which I can't seem to find using google right now.