PowerTag Disable Alarms

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Boris_Horvat
Ensign
Ensign
0 Likes
8
860

PowerTag Disable Alarms

Hello.

 

I have more PowerTags and one PowerTag Link.

In web page of PowerTag Link there are some preconfigured alarms.

For example: Current Alarm 45% of the Nominal Current.

I deleted all alarms from settings --> alarms.

No alarms should be triggered, but this (> 45%) alarm still appears.

Any idea how to disable this?

 

Best regards, Boris.

Tags (1)

Accepted Solutions
Thierry_Baudard
Lieutenant Lieutenant
Lieutenant
0 Likes
3
812

Re: PowerTag Disable Alarms

Hello,

 

This 45 % alarm is available in the bit 3  of the modbus register 3300.

I have made a test in my lab and also observe the bug that you mention with the last fw available 2.1.5

Unfortunately, you are rigth : It is possible to disable the 0%,50%, 80% current alarm in the alarm settings but the 45% current alarm cannot be disabled and alway appears in web page !

 

I will push the bug to the R&D team

 

BR

 

 

 

 

 
 

 

Thierry BAUDARD
Digital Power Technical Pre sale support International Hub

See Answer In Context

Tags (1)
8 Replies 8
Romain_Polette
Sisko Sisko
Sisko
0 Likes
5
853

Re: PowerTag Disable Alarms

Hello @Boris_Horvat , 

 

What is the Firmware version of your PowerTag Link ?


Please go under SETTINGS -> DEVICES --> WIRELESS DEVICES.

 

Then check the following settings for your PowerTag Sensors:

  • Associate Breaker Rating

Ensure that this setting is matching your breaker current rating.

 

Regards, 

 

Romain POLETTE - Solution architect - France Operation
Intencity - Grenoble - France
Tags (1)
Boris_Horvat
Ensign
Ensign
0 Likes
4
846

Re: PowerTag Disable Alarms

Hello @Romain_Polette.

 

FW version of PowerTag Link is 002.001.005.

 

Associate Breaker Rating is correctly set.

But the problem is, that there is no defined alarm, but "Current Alarm 45% of the Nominal Current" triggered all the time.

 

Best regards.

Tags (1)
Thierry_Baudard
Lieutenant Lieutenant
Lieutenant
0 Likes
3
813

Re: PowerTag Disable Alarms

Hello,

 

This 45 % alarm is available in the bit 3  of the modbus register 3300.

I have made a test in my lab and also observe the bug that you mention with the last fw available 2.1.5

Unfortunately, you are rigth : It is possible to disable the 0%,50%, 80% current alarm in the alarm settings but the 45% current alarm cannot be disabled and alway appears in web page !

 

I will push the bug to the R&D team

 

BR

 

 

 

 

 
 

 

Thierry BAUDARD
Digital Power Technical Pre sale support International Hub
Tags (1)
Boris_Horvat
Ensign
Ensign
0 Likes
0
761

Re: PowerTag Disable Alarms

Thanks for info.

 

Best regards, Boris.

Tags (1)
SESA648446
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
1
655

Re: PowerTag Disable Alarms

Hi @Thierry_Baudard 

 

Recently I also received feedback from a customer regarding this problem. Wondering do you have any updates from R&D? Thank you

 

Best regards,

 

Tags (1)
Romain_Polette
Sisko Sisko
Sisko

Re: PowerTag Disable Alarms

Hello @SESA648446 , 

R&D is actively working on the topic.
I will have more information soon.

Regards, 

Romain POLETTE - Solution architect - France Operation
Intencity - Grenoble - France
Tags (1)
Romain_Polette
Sisko Sisko
Sisko
0 Likes
1
495

Re: PowerTag Disable Alarms

I forgot something important.

 

With PME you have the possibility to deactivate the 45% alarm. This workaround is not possible for the "Zero Current" Alarm.

 

Please go on system\translators => copy all PowerTagxxx.ion and .xml files.

Past them on config\translators

Go on system\translators\events => copy PowerTag.evt

Past the .evt file on config\translators\events

Open the config\translators\events\PowerTag.evt file with a text editor.

 

Check the line: <EventInfo ID="2502" Priority="128" Enabled="YES" Comment="Current Alarm (45%)" />

Change the parameter to Enables = "NO"

 

Restart ION Network Router and associated Services.

Restart ION Application Modules Services.

 

Regards, 

Romain POLETTE - Solution architect - France Operation
Intencity - Grenoble - France
Tags (1)
SESA648446
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
433

Re: PowerTag Disable Alarms

Hi @Romain_Polette 

 

Thanks for your information and please let me know if you have any updates from R&D. Thank you.

 

Best regards,

 

Tags (1)