【PM8240】Regarding "maximum values" of current and voltage THD

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • 【PM8240】Regarding "maximum values" of current and voltage THD
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Miyai
Lieutenant Miyai
Lieutenant

Posted: ‎2023-03-08 03:56 PM

0 Likes
3
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-08 03:56 PM

【PM8240】Regarding "maximum values" of current and voltage THD

Hello,

 

What is the maximum value for Modbus communication regarding THD(V, I)?

 

I understand that the Modbus definition is in FLOAT32 format and the maximum value is 3.402823466 x10^(38).

 

However, I don't think PM8000 outputs such a large value, so if there is an upper limit, please let me know.

 

 

Best regards,

Miyai

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2023-03-08 07:31 PM

1 Like
1
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-08 07:31 PM

The default shipping configuration for the Harmonic Measurement Modules is to show THD as a Percentage ratio of the measured rms harmonic distortion and the fundamental.

The "Percentages" option behaves the same as "Percent Fundamental" when the "Max Demand" input is left unlinked (as done by default on all modules). To prevent a divide-by-zero, this calculation is skipped and a 0 value returned when the fundamental (denominator) is below the "force level" (0.01% of FS on current and by default 0.02% of FS on voltage). Based on this, I suspect the theoretical upper bound is on the order of 1,000,000% when full scale harmonics and a very small non-zero fundamental are present.

The "Percent RMS" option effectively normalizes results to 100% (100% is the maximum possible value because the denominator includes all the harmonic signal)

Screenshot 2023-03-08 191214.png

https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=HarmonicsMeasurementModule...

 

See Answer In Context

Reply
Replies 3
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-03-08 04:45 PM

0 Likes
0
1401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-08 04:45 PM

Hello @Miyai ,

 

The THD can be greater than 100%, so the limit of floating point kind of is the maximum theoretical limit the number can get to. To get a number this big would require a system with almost no fundamental signal and a huge harmonic signal, to not really practical to see a number that large. Can't really give a practical limit.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2023-03-08 07:31 PM

1 Like
1
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-08 07:31 PM

The default shipping configuration for the Harmonic Measurement Modules is to show THD as a Percentage ratio of the measured rms harmonic distortion and the fundamental.

The "Percentages" option behaves the same as "Percent Fundamental" when the "Max Demand" input is left unlinked (as done by default on all modules). To prevent a divide-by-zero, this calculation is skipped and a 0 value returned when the fundamental (denominator) is below the "force level" (0.01% of FS on current and by default 0.02% of FS on voltage). Based on this, I suspect the theoretical upper bound is on the order of 1,000,000% when full scale harmonics and a very small non-zero fundamental are present.

The "Percent RMS" option effectively normalizes results to 100% (100% is the maximum possible value because the denominator includes all the harmonic signal)

Screenshot 2023-03-08 191214.png

https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=HarmonicsMeasurementModule...

 

Reply
Miyai
Lieutenant Miyai
Lieutenant

Posted: ‎2023-03-09 05:25 PM

0 Likes
0
1376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-09 05:25 PM

Hello @DanL , @Charles_Murison ,

 

Thank you for advice.


I will reply to the customer with the maximum value of the float.

If the customer wants to narrow the upper limit again, I will answer with 1,000,000%.

 

Best regards,

Miyai

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of