ION9000 FCAS window monitoring

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
alannavial
Crewman Crewman
Crewman
0 Likes
2
328

ION9000 FCAS window monitoring

One of the strictest FCAS requirements we need to meet as per the attached is that when there is a frequency deviation outside of a certain range (for example of the grid frequency drops below 48.8hz) then we need to capture 60s of data after the trigger point but also 5s before (in 20ms granularity).

alannavial_0-1659678772070.png

 

 

Referring to the manual attached for the ION9000 on page 217 there is information on ‘Extended Waveform Capture’

alannavial_1-1659678772164.png

 

 

How long can the C and D periods in the above diagram be and how easy can the values be changed? We need the pre event period to be 5s and the post event recording to be 60s.

 

Can the ION9000 easily be configured to capture such events?  If so, how would I do this?

 

Tags (2)

Accepted Solutions
DanL
Commander Commander
Commander

Re: ION9000 FCAS window monitoring

That one bullet point looks like it is from Australian FCAS requirements?

If so the context matters, because that requirement is not for instantaneous voltage (ie. waveform capture), but instead for co-incident "high-speed" frequency and power measurements.
I would recommend using a setpoint module to trigger a DataRecorder configured with pre-trigger and post-trigger records.
https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=DataRecorderModule-21B4C52...

With the DataRecorder's inputs linked to The HighSpeed PowerMeter module's "HS Freq" and "HS kW tot" outputs, it will collect data every half-cycle.
For example:
Pre-Trigger records = 500 (5s)

Post-Trigger records = 6000 (60s)

Buffer Depth = 13002 (two full captures fully buffered)

Depth = 65010 (internal storage for 10 full captures)

See Answer In Context

Tags (1)
2 Replies 2
DanL
Commander Commander
Commander

Re: ION9000 FCAS window monitoring

That one bullet point looks like it is from Australian FCAS requirements?

If so the context matters, because that requirement is not for instantaneous voltage (ie. waveform capture), but instead for co-incident "high-speed" frequency and power measurements.
I would recommend using a setpoint module to trigger a DataRecorder configured with pre-trigger and post-trigger records.
https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=DataRecorderModule-21B4C52...

With the DataRecorder's inputs linked to The HighSpeed PowerMeter module's "HS Freq" and "HS kW tot" outputs, it will collect data every half-cycle.
For example:
Pre-Trigger records = 500 (5s)

Post-Trigger records = 6000 (60s)

Buffer Depth = 13002 (two full captures fully buffered)

Depth = 65010 (internal storage for 10 full captures)

Tags (1)
alannavial
Crewman Crewman
Crewman

Re: ION9000 FCAS window monitoring

Hi Dan,

Thank you for the help.  You answered my question perfectly!