Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Have you notice distorted values display on PM meters?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Have you notice distorted values display on PM meters?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All
Related Products
product field
Schneider Electric
PowerLogic PM5000 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
Emilie_Ernwein
Ensign Emilie_Ernwein Ensign
Ensign

Posted: ‎2023-03-27 05:33 AM . Last Modified: ‎2023-04-03 12:25 AM

0 Likes
0
805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-03-27 05:33 AM

Have you notice distorted values display on PM meters?

Schneider electric PMxxxx and their efficient running rely largely on the connected Current Transformers, their installation and their calibration.

CTs are sensors sending electrical signal to the PMxxxx which then perform the calculation of your power quality and the subsequent value display.

Consequently, whether your CTs are not properly connected or calibrated, harmonics may be polluted, and value distortion could then be observed on your PMxxxx display.

 

But how can we prevent these disfunctions?

First of all, the CTs should be chosen according to wires and PMxxxx specification:

schema.png

  • PM input current
  • PM accuracy class
  • Cable size and load
  • Voltage connection
  • Space between current transformers

 

 

Also note that common failure causes through the installation could be:

  • CTs connection to the PMxxxx
  • PMxxxx calibration
  • Degradation of the CTs*

Our range of Current Transformers:

Schneider Electric offers a large range of Current Transformers fully compatible with Schneider Electrics and Third-Party measurement devices. Our range is divided in two collection:

  • Solid core current transformers, perfect for new installation
  • Split core current transformers, perfect for retrofit

Discover more about our CTs and their features

solid core.png

 

Solid core CTs                             Split core CTssplit core.png

 

 

 

 

 

 

 

 

*With time, CTs can deteriorate and engender accuracy variability. All CTs are not equal in durability

  • Thumbnail of PowerLogic PM5000 series
    Schneider Electric
    PowerLogic PM5000 series
View products (1)
Labels
  • Labels:
  • Did you know
  • PM Announcements
  • PM3000
  • PM5000
Tags (4)
  • Tags:
  • energy efficiency
  • energy monitoring
  • english
  • power metering
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of