84528members
353773posts
MP130-24M Actuators Always giving 10 Volt Feedback.
Field Devices Forum
Collaborate with a community of professionals and find answers and discuss anything related to the Field Devices (Sensors, Thermostats, Valves & Actuators and more)
Nick_Ortlipp
Crewman Crewman
1899
I have 10 + MP130-24M Actuators installed on a project. All are giving ten volt feed back no mater what the signal is. The feed back only modulates (10 volts- 0 Volts-10 -Volts) When the reset button is pushed. All cables and signals have been proven. I thought it may have been a faulty one at first but each successive actuator has the same issue. MP500 and MP300 installed all work perfectly.
Any ideas on a fix would be greatly appreciated.
Simon_Firth
Ensign Ensign
Re: MP130-24M Actuators Always giving 10 Volt Feedback.
the MP130 actuator with feedback is the MP130-24MP
P for position feedback.
You need to first ensure the actuator is mounted on the valve, powered and calibrated. Output X is not correct until the actuator is calibrated.
You may need to reset the actuator for it to re-calibrate, and this reset is recommended if the manual override is ever operated.
There is a small push button on the PCBA next to the Dip-switches that re-sets the actuator.
Specification sheet attached
Mr Valve
4 Replies 4
FirdousKhan
Community Alumni (Retired)
Hi the community members can you help this member on this topic please?
@WaynePeters or @DavidChild do you think you can advice on this topic?
@Nick_Ortlipp, in the meantime, please check the Knowledge base, maybe you can find useful information.
But if you still in the same situation please do not hesitate to inform us here.
Have a nice day.
Best,
Firdous - Animation and Moderation Exchange Community Team
DavidChild
Sisko Sisko
Sisko
2
1879
Looking at the install sheet, these don't have feedback....unless I've missed something!
24Vac
Y = 0-10V or 0(4)-20mA control signal
Common
Simon_Firth
Ensign Ensign
Mr Valve
Nick_Ortlipp
Crewman Crewman
Thanks for the feedback.
It looks like what the issue is, I was commissioning the plant before the chilled water was running. Once a pressure was in the pipes and a reset/power cycle was done on the actuator, the valves stroked and started giving the correct feedback.
I am a bit worried that with intermittent loss off chilled water pressure which happens often during the commissioning phases of construction, I may have to run around site and reset this model.