Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Satchwell BAS & Sigma
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,834
  • TAC IA Series 1,820
  • TAC INET 1,458
  • Field Devices 720
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 45
  • EcoStruxure Building Advisor 12
  • EcoStruxure Building Activate 7
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "satchwell bas & sigma"

View in: "Building Automation Knowledge Base" | Community

474 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 24
  • Next »
Label: "Satchwell BAS & Sigma" Show all articles

Software and Firmware compatibility matrix for older versions of the traditional product lines

Issue Current information will be stored and updated in release notes and online documentation. Compatibility Matrix of Operating Systems, Video, Product Announcements, SQL Compatibility Product Line Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Windows Operating Systems and iBMS (intelligent Building Management System) Software Cause Compatibility, Firmware, Product Announcements Resolution Please see release documentation for current and recent products. For the Firmware compatibility matrix for: I/NET, it is available HERE or the EcoBuilding Download Center Continuum, click HERE Xenta Software Downloads HERE Vista, click HERE EcoStruxure Building Operation, click HERE Product Announcements can be a great tool for discovering which products have been tested and are compatible with the different versions. These documents are available on the Extranet, but have been compiled here for ease of access: I/NET 2.40   Product Announcement 2.41   Product Announcement 2.41a Product Announcement 2.42   Product Announcement and Compatibility Matrix (page 5) 2.43   Product Announcement PA-00239 2.44a Software Available from Exchange Download Center 2.45   Software Available from Exchange Download Center 2.46 Software Available from Exchange Download Center 2.47 Software Available from Exchange Download Center 2.47a Software Available from Exchange Download Center 2.47b Software Available from Exchange Download Center 2.48 Software Available from Exchange Download Center Operating Systems and SQL Supported Video Compatibility Support Policy PA-00279 Software Support for TAC I/NET Continuum v1.92 Product Announcement v1.93 Product Announcement v1.94 Product Announcement PA-00210 1.94 SP1 Product Announcement PA-00273 1.9 - 2.1 Software, Firmware, & Video Compatibility Matrix Concerning IE10 and IE11 browser support  2.0 Feature Blast 2.0 + 2.01/ 2.02 Update Compatibility Matrix 2.0  Product Announcement PA-00353 2.0 CyberStation Installation Guide 2.0 WebClient Installation Guide 2.0 Software License and Ordering Activation Process 2.0 Software and Controller Upgrade Process Andover Continuum PA-00333 Support Policy PA-00272 for Andover Continuum Vista v5.1.5 Product Announcement v5.1.6 Technical Product Advisory v5.1.7 release note document, TAC Vista Compatibility Matrix, SNVT Matrix documents, and TPA-VSTA-11-0020.00 v5.1.7 Product Announcement x5.1.8 Release Note TAC Vista 5.1.8 and TAC Xenta 500/700/900 5.1.8 v5.1.9 Vista Compatibility Matrix SecurityIAS Product Announcement PA-00291 Product Announcement TAC Vista transition to SmartStruxure solution overview  Support Policy PA-00274 for TAC Vista Satchwell Sigma v4.05 SEB Release Notes v4.06 Release Notes v4.06 Release Note Supplement v4.07 Release Notes Satchwell Sigma Standard Edition Installation and User’s Guide Support Policy PA-00297 for Satchwell Sigma v4.08 Release Notes PA-00397 Sigma Version 4.08 Sigma server on a virtual machine Satchwell Micronet data sheet - MicroNet View 2.1 OS Compatibility - Micronet View PA-00228 Product Announcement Support Policy PA-00298 for Satchwell MicroNet PA-00228 Satchwell MicroNet End of Commercialization Announcement I/A Series PA-00163 I/A Series R2 & G3 Product Announcement PA-00114 Legacy Products Windows 7 Compatibility I/A Series R2 with Windows Compatibility Chart PA-00243 Software Product Update - Q2 2013 PA-00251 Hardware Product Update - Q2 2013 PA-00278 Software Product Update - Q3 2013 I/A Series (Niagara) R2 Windows Compatibility Matrix with additional detail I/A Series (Niagara) AX/G3/N4 Windows Compatibility Matrix with additional detail Support Policy PA-00280 R1 for TAC I/A Series StruxureWare Building Operation Please visit Maximum number using StruxureWare Building Operation (Scalability and Capacity) SmartStruxure Lite Please visit SmartStruxure Lite solutions
View full article
Picard Product_Support
‎2018-09-07 07:37 AM

Last Updated: Guinan RandyDavis Guinan ‎2025-01-23 12:55 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • TAC IA Series
  • TAC INET
  • TAC Vista
15172 Views

BMS Redundancy TVDA

Issue How to be redundant with your intelligent Building Management System (iBMS) Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell Sigma, Security Expert, TAC INET Environment Existing intelligent Building Management System Open Mind High Availability Solutions (Deprecated by manufacturer) everRun MX ztC Edge Cause In engineering, redundancy is the duplication of critical components of a system with the intention of increasing the system's reliability. To be redundant with an intelligent Building Management System (iBMS) would take on two possibilities. Have an alarm on critical points alerting personnel who move into action quickly replacing control boards or devices in the event of failure. Have secondary backup controllers which upon failure, which are used to control devices resuming functionality. This is accomplished through programming the BAS with event sequences triggered from alarms or flags noting the failure. Redundancy capabilities and feasibility are site specific. Ascertaining failure in boards, points, or devices is crucial to creating secondary measures to keep seamless processes going and resume with functions.   Error detection and correction with maintenance is often the best practice for preventing failure. Worn components are the leading cause of failure, followed by a lack of planning and consideration in the protection of electrical components through power surges or failures.   For the database, backups including automated backups for MSDE, SQL Express, and Full SQL are available. For further information on database backups and options, take a look at Microsoft SQL Management Studio. For Host Computer backups, look at adding a secondary computer which replicates the database and can capture transactions and messages should a failure with the primary host computer take place. Also work with the local IT department to keep machines up to date, safe, and clean of 3rd party applications which may interfere with integrity. Schneider Electric’s building management systems are designed such that building control continues even when controller to server communication is disrupted. The BMS server is home to a database of alarm and historical data, as well as system parameters and programs. When a server or its network connection fails, the collection of data from building controllers halts until the problem is resolved. For data critical applications, this solution provides an environment capable of preventing the data loss that results from these types of failures.  Although we do support its use with EcoStruxure Building Operation, Security Expert, Continuum, I/NET, Vista, Sigma, and I/A Series as a disaster recovery solution, we do not provide direct support for EverRun. Resolution For Open Mind High Availability Solutions guide please look at the following link; Open Mind High Availability Solution guide For everRun MX solution guide please look at the following link; everRun MX guide For ztC Edge solution guide please look at the following link; ztC Edge guide   
View full article
Picard Product_Support
‎2018-09-06 01:43 PM

Last Updated: Shuttle Bay DanielBergman Shuttle Bay ‎2024-10-24 11:11 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
  • Field Devices
  • Satchwell BAS & Sigma
  • TAC INET
5287 Views

How to identify what ports are being used on a PC

Issue How to identify what ports are being used on a PC. Product Line All product Lines. Environment Any Windows OS Cause Running multiple applications on the same PC without managing TCP/UDP port assignments can lead to conflicts. Resolution TCPView will help you identify all ports and services to each application. Download from Microsoft's website http://technet.microsoft.com/en-us/sysinternals/bb897437.aspx Detailed instructions are available at the site.
View full article
Picard Product_Support
‎2018-09-10 01:28 PM

Last Updated: Spock Mahmoud_Sayed Spock ‎2024-05-22 01:21 AM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
1862 Views

Sigma parallel port dongle or USB dongle upgrade to SBO/EBO software license exchange.

Issue Sigma parallel port dongle or USB dongle upgrade to software license Product Line Satchwell Sigma Environment Sigma version 4.08 Cause It is difficult to purchase computers with parallel ports. With the use of virtual computer operating systems, USB ports may not be available either. ∴ A different type of Sigma licensing will be required. Resolution Please note: EBO 3.x has now entered into its limited support period with Sigma support coming to an end, this free of charge service, provided by PSS in good faith, will no longer be available from the 1st May 2024. Any remaining Sigma systems will need to continue to use their current licensing method or be upgraded to EBO.   Product Support can arrange for an upgrade from your existing parallel port or USB type Sigma dongle to a Building Operation software license entitlement for Sigma 4.0.8. Sites running Sigma software 4.07 or older where support for software licensing isn't available need to be upgraded to Sigma version 4.08.57 or later to use the software option. Sigma Software license type availability is documented on page 8 in the Sigma 4.08 release note.   For engineers using Sigma 4.08: The Building Operation Evaluation License, available from the Schneider Electric Download Center, will unlock the Sigma 4.08 for testing etc for the period of the Evaluation License (maximum 3 months or until the expiry of the downloaded license).   Unlock Sigma software using the Building Operation Evaluation License. To install the software licensing option for Evaluation License: - Stop the Sigma server service. Install Building Operation License Administrator. Add Evaluation License file to the Building Operation License Server. Start the Sigma server service. Sigma should now be licensed. For customer sites using Sigma 4.08: To reduce the Sigma system downtime, Install the Building Operation License Server version 1.6 or later. (it is recommended that the latest available version of the Building Operation License Server compatible with the computer's operating system is used). Dongle Upgrade Procedure: Download the Sigma Dongle Replacement - Required Data 2020 form. Complete the cells that are highlighted/filled in blue. Open a case with your local support team.. Supply the completed spreadsheet. The Product Support representative that is assisting you with your license upgrade, will contact you and provide the address and details where to send the site's Sigma dongle. Once the dongle has been received a software license will be ordered and then the software license entitlement for Sigma will be sent to you. If the site is a standalone Sigma site, Product Support will need to get approval from the regional category manager before escalating for the software license.   To install the software licensing option for Sigma 4.08: - Stop the Sigma server service. Install Building Operation License Administrator. Add the entitlement to the Building Operation License Server. Start the Sigma server service. Sigma should now be licensed.   Note: If your current Sigma dongle contains Remote Alarm Manager licensing, Remote Alarm Manager does not support the Building Operation license server option. The USB dongle can still be used or a TAC license server type license can be used instead of the dongle.
View full article
Picard Product_Support
‎2020-12-15 02:24 AM

Last Updated: Gary Schneider Alumni (Retired) ‎2024-03-19 07:23 AM

Labels:
  • Satchwell BAS & Sigma
7337 Views

Side-by-side error when starting SigmaX, RegSigmaX or SigView

Issue The following errors are seen when trying to run SigmaX, RegSigmaX or SigView.  The application has failed to start because its side-by-side configuration is incorrect. Please see the application event log or use the command-line sxstrace.exe tool for more detail.  Application event log: Activation context generation failed for "C:\SigmaX\Bin\RegSigmaX.exe". Dependent Assembly Microsoft.VC80.MFC,processorArchitecture="x86",publicKeyToken="1fc8b3b9a1e18e3b",type="win32",version="8.0.50727.762" could not be found. Please use sxstrace.exe for detailed diagnosis. Product Line Satchwell Sigma Environment SigmaX 7.0.6 on Windows 7 32-bit SigmaX 7.09 on Windows 10 64bit SigView Cause Microsoft Visual C++ 2005 redistributable has not been installed. It appears that SigmaX requires this version to run. Resolution Either the Microsoft C++ 2005 is not installed, or if it is, then the Service Pack 1 (SP1) is required to be installed. This can be checked under the Windows 'Apps and Features'. Install Microsoft Visual C++ 2005 SP1 Redistributable Package (x86). In some cases,  Microsoft Visual C++ 2005 SP1 Redistributable Package Security Update (x86) is required to resolve the issue. The 32bit (x86) version should be installed if installing Microsoft Visual C++ 2005 SP1 does not fix the problem. 
View full article
Picard Product_Support
‎2018-09-11 01:47 PM

Last Updated: Gary Schneider Alumni (Retired) ‎2024-03-06 04:07 AM

Labels:
  • Satchwell BAS & Sigma
4087 Views

Test the network card of a PC

Issue The network card is not working on the PC.  Product Line Andover Continuum, EcoStruxure Access Expert, EcoStruxure Building Expert, EcoStruxure Building Operation, EcoStruxure Security Expert, Satchwell BAS & Sigma, Satchwell MicroNet, TAC IA Series TAC I/NET, TAC Vista Environment PC Network Interface Card Cause Require a method to test the network card. Resolution Assuming you have the correct protocols loaded:- Open up a command prompt and type ‘ipconfig’(1) then press enter to get a list of the available network cards. Find the specific network card by name (2) Record the IP Address (3) assigned to the card, e.g. 192.168.5.90 If the card is unplugged (4) connect a network cable and start back at step 1 If the network card does not appear in Device Manager check the drivers are correctly installed for the card and when installed correctly start back at step 1. If the network card still does not appear it could be disabled.  In Network Connections right click the adaptor and select Enable (5) and start back at step 1. After these steps if the network card still does not appear when running ipconfig it is most likely damaged. If/when an IP Address is successfully obtained open a Command Prompt and type ping followed by the IP Address of the card, for example ping 192.168.5.90 (1). A functioning card will respond with 4 successfully replies (2) and the associated statistics (3) As additional information a good first step would be to "ping 127.0.0.1". This will not test a network card but indicates that the TCP/IP protocol is installed and functioning on the host PC.
View full article
Picard Product_Support
‎2018-09-06 03:27 PM

Last Updated: Admiral GavinHe Admiral ‎2024-01-25 08:06 AM

Labels:
  • Andover Continuum
  • EcoStruxure Access Expert
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
1747 Views

Ethernet connection speeds for Sigma controllers

Issue Which Ethernet port speeds are supported by Sigma controllers? Product Line Satchwell Sigma Environment Sigma controllers Ethernet New Hardware. ARM 7(S-696, S-x96CPU-AE, S-796, S-x796CPU-AE, S-DNN3, S-DNN3-DT, S-632-E, S-632-AE and S-IC3's) Old Hardware V53  (S-ETH, S-496, S-596, S-532, S-DNN and S-IC's) Cause The newer ARM-7 controller hardware supports more Ethernet connection speeds than the older V53 controller hardware. Resolution Most Ethernet hubs or switches autoscan to find the best connection speed.  For Sigma device hardware types, the supported Ethernet speeds are as follows: ARM-7 (New hardware): 100Base-T (and supports port auto-scanning on connection) 100M Half Duplex 10M full/half duplex V53 (Old hardware): 10Base-T (does not support port auto-scanning) 10M half Duplex Additionally, for direct connections to a Sigma controller: ARM-7 Ethernet connection supports both straight and cross-over Ethernet cables. V53 hardware only supports cross-over cables.
View full article
Picard Product_Support
‎2018-09-06 02:14 PM

Last Updated: Administrator CraigEl Administrator ‎2023-11-13 06:04 PM

Labels:
  • Satchwell BAS & Sigma
1585 Views

Sigma transition to Building Operation - Alarms not received at the Enterprise Server

Issue Alarms not received at the Enterprise Server Product Line EcoStruxure Building Operation, Satchwell BAS & Sigma Environment Sigma Transition Alarms Cause Alarms are being generated by the controller but do not appear at the Enterprise Server. Resolution If any changes are made to the Sigma system using the Sigma Server, then either all, or part of the Sigma configuration must be re-imported into the Building Operation Enterprise Server.
View full article
Picard Product_Support
‎2018-09-06 09:14 AM

Last Updated: Administrator CraigEl Administrator ‎2023-10-26 03:54 PM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
1245 Views

Temperature Sensor Resistance Charts

Issue Temperature Sensor Resistance Charts Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Temperature Sensors Cause Temperature (°C) to Resistance Charts (ohms). Upgrading the site BMS, but retaining the existing sensors and the sensor resistance values are not known. Resolution The resistance of a sensor at a specific temperature can be downloaded below, there are a number of tables collated from different sources for a number of Schneider Electric sensors and other BMS suppliers.   In EBO, the thermistor selection in the IO module or controller does not represent the thermistor bead type, an example is the Continuum Type I in EBO, but the bead is a Type 3,. For further information regarding this see the KB article  Thermistor type selection in EBO.   The document All Sensors covers the following:   Satchwell DxT sensors are replaced by STR600, STP660, STD600, STO600 type T with shunt, and use the Satchwell T range chart Drayton DC1000, DC1100 30K6A1 is now known as STR600D, STP600D, STO600D Andover 10K4A1 TAC Inc. Vista 1.8KA1 I/A series 10K3A1 with 11K shunt INET 10K2A1 (10k Dale) BALCO 1000 ohm RTD   Older Satchwell ranges: Satchwell DW1204, DW1305, DWS1202 Satchwell DO Satchwell DD/DR Other manufacturers included: Allerton 3K3A1 Ambiflex 2012, Honeywell Aquatrol, Jel/Thorn, Trend, York 10K3A1 Schlumberger (air) 5K3A1 Schlumberger (immersion) 100K6A1 Automatrix, York, Sibe 10K4A1 Honeywell 20K6A Landis & Gyr PT100A, PT1000A   Further information regarding INET, IA, the document Thermistor Types Tables (Veris Industries) is available.  The 1k Balco resistance chart is also available.   Further information for the Continuum ACC Temp 10K Type 3 also known as 10K4A1, the document Thermistor Temp Resist Chart (Precon Thermistors) is available.   TC900 series TC900 RS-03 sensor chart   For I/A Series Controllers (MNL/MNB) Compatible sensors that have a built-in 11k shunt resistor include the TS-5711-850 TS-57011-850 TS-57031-850 TSMN-90110-850 Series Any sensor that matches resistance to temperature curve for a 10K Thermistor Type G (U.S. Sensor), Type 9 (Dale/Vishay) or Type III (ACI Series AH) can be used with the I/A Series MNL and I/A Series MNB series controllers, provided that a 11k ± 0.1% 1/8 watt resistor is wired in parallel with the sensor. The input has a range of -10 to 135 °F (-23.3 to 57.2 °C) with an accuracy of ±1% of span. Temperature / Resistance Reference Values Temperature Deg F (Deg C) Resistance Resistance Incl. 11k Shunt 32 (0) 25490 8,012 68 (20) 12,260 5,798 75 (25) 10,000 5,238 104 (40) 5,592 3,707 140 (60) 2,760 2,206 The full temperature/resistance table for the US Sensor 10K Thermistor R-T Curve Type G sensor. Please note that the controller may not be able to use the full temperature range shown in the table.  
View full article
Picard Product_Support
‎2020-12-02 06:46 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-27 04:23 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
25151 Views

Using a USB - serial lead to SDCU a controller.

Issue Using a USB - serial lead to SDCU a controller. Product Line Satchwell Sigma Environment Satchwell Sigma Controllers SDCU Cause My Laptop does not have a serial port.  Can a  USB - serial lead be used to SDCU a controller. Resolution A USB - serial RS232 can be used. Plug the lead in to the laptop. For 1st time use, install the driver that comes with the lead. Goto My Computer > View System Information > Hardware > Device Manager > Ports and check the port number assigned (this may change each time the lead is plugged). Use the SDCU lead and plug this between the USB - serial lead and the controller. Open SDCU utility and set the port to that seen in item 3. Configure controller. Pinouts for the SDCU cable is as follows:
View full article
Picard Product_Support
‎2018-09-06 01:22 PM

Last Updated: Administrator CraigEl Administrator ‎2023-09-20 09:49 PM

Labels:
  • Satchwell BAS & Sigma
1629 Views

Sigma Username and Password encryption

Issue Are username and passwords encrypted during transmission from the remote client or the web client to the Sigma server? Product Line Satchwell Sigma Environment Sigma Remote Client WebClient Cause Are username and passwords encrypted during transmission from remote client to the Sigma server? Are username and passwords encrypted during transmission from web client to the Sigma server? Resolution Usernames are not encrypted during HTTP transmission from the remote client and web client to the Sigma server. Passwords are encrypted during HTTP transmission from the remote client and web client to the Sigma server.
View full article
Picard Product_Support
‎2018-09-06 12:46 PM

Last Updated: Administrator DavidFisher Administrator ‎2023-09-11 01:47 AM

Labels:
  • Satchwell BAS & Sigma
2708 Views

License server port used to reach Building Operation licensing server

Issue Firewall issues when trying to reach out to the activation server for a license Product Line EcoStruxure Building Operation, Satchwell Sigma, TAC Vista Environment Building Operation Licensing Firewall Cause If the corporate network has a very restricted firewall policy or rules, the port needed to reach and activate a license may be blocked. Note: The same license server is used for EcoStruxure Building Operation, Satchwell Sigma and TAC Vista software licenses. Resolution Open Port 443 (HTTPS) for the server hosting the license server, and ensure that the routing paths to the Flexnet Licensing server URL's are all fully open. The Licensing Server URL should be opened from the site, and it is: https://schneider-electric.flexnetoperations.com If the site of the old server has issues with the non secure communications or the communications forwarding between the previous and the new server, there is a tool available to configure EBO to only use the new server. See the Exchange Community article for the download: SBO License Setup Note: From EBO V2.0 only the new license server is used, port 80 is no longer required and HTTP is redirected to HTTPS.
View full article
Picard Product_Support
‎2021-02-17 02:51 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2023-09-11 01:28 AM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • TAC Vista
11355 Views

Offer Creation Roadmap

Issue What new features are planned for inclusion in future product releases? Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell BAS & Sigma, Satchwell MicroNet, TAC IA Series, TAC INET, TAC Vista, EcoStruxure Access Expert, EcoStruxure Security Expert Environment All product ranges Cause Information required on future Product Marketing plans. Resolution This document is no longer published on the Download Center by Product Management. For further information on the future product planning please contact the Product Manager for the specific product in your region. Americas: Americas.EcoStruxureBuilding@schneider-electric.com EMEA: EMEA.EcoStruxureBuilding@schneider-electric.com Asia Pacific & India: AsiaPac.EcoStruxureBuilding@schneider-electric.com
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Last Updated: Administrator CraigEl Administrator ‎2023-08-20 05:37 PM

Labels:
  • Andover Continuum
  • EcoStruxure Access Expert
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
2792 Views

Virtual License for Sigma 4.08 - License Server 'Unable to connect to "Server"'

Issue With a Sigma 4.0.8 installation using a software license, when adding the entitlement ID to License administrator. The message “Unable to connect to "Server" is displayed. Product Line EcoStruxure Building Operation Environment Enterprise Server Sigma License administrator Cause When adding the Sigma entitlement ID to EBO License administrator, an internet connection is required to allow the license administrator to connect to the on-line licensing server. Resolution When a PC is not connected to the internet, and you need to activate a software license entitlement, an Offline Activation Tool is available, this can be downloaded here.
View full article
Gary Schneider Alumni (Retired)
‎2023-04-28 07:24 AM

on ‎2023-04-28 07:24 AM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
1448 Views

Identify the Sigma version or build number installed on a computer

Issue The ability and procedure to identify the version of Sigma software on a system. Product Line Satchwell Sigma Environment Release number: 1, 2, 3, 3.1, 3.3, 3.4, 3.6, 3.7, 3.7 SP2, 3.7 SP3, 3.10, 3.11, 4.00, 4.00 SP2, 4.00 SP4, 4.01, 4.01 SP1, 4.01 SP3, 4.01 SP4, 4.01 SP4a, 4.01 SP5, 4.02, 4.03, 4.03 SP1, 4.04, 4.04 SP1, 4.04 SP2, 4.04 SP3, 4.05, 4.05 SP1, 4.05 SP2, 4.05 SEB, 4.06, 4.07, 4.07 SP1, 4.07 SP2, 4.08 Build number: 1.52, 2.13, 3.12, 3.17, 3.3, 3.31.1, 3.32.10, 3.33.9, 3.33.11, 3.33.13, 3.34.11, 3.34.11, 3.36.11, 3.36.16, 3.36.20, 3.37.08, 3.37.09, 3.37.12, 3.37.13, 3.37.16, 3.37.18, 3.39.09, 3.40.06, 3.40.09, 3.41.14, 3.41.15, 3.41.16, 3.41.18, 3.41.19, 3.42.34, 3.42.43, 3.42.48, 3.43.18, 3.44.14, 3.44.16, 3.44.18, 3 45 48, 3 45 51, 3 45 58, 3.46.57, 3.46.62, 3.46.70, 3.46.72, 3.46.73, 3.46.79, 3.46.80 3.46.81, 3.46.85, 3.46.86, 3.46.89, 3.46.98, 3.46.104, 3.46.105, 3.46.107, 3.46.108, 3.46.110, 3.46.111 Cause Software installed is identified with a build number and not a release number. Resolution To view the Sigma build number, using a Sigma client running locally on the Sigma server, select About System Manager from the Help menu. The displayed window shows the Sigma release and build number Refer to the table below to find the Release No. Sigma Release No. Build No. Software/Firmware File Date   SigmaX   Release 1 1.52 Software/Firmware 22.06.2001 SigmaX 4.5 Release 2 2.13 Software/Firmware 14.02.2002 SigmaX 5.2 Release 2 3.12 Supplement 14.02.2002 SigmaX 5.2 Release 3 3.12 Software 31.07.2002 SigmaX 5.2 Release 3.1 3.17 Software 17.09.2002 SigmaX 5.2 Release 3.3 3.3 Software 30.07.2003 SigmaX 5.2 Release 3.4 3.31.1 Software 03.10.2003 SigmaX 5.2 Release 3.6 3.32.10 Software 19.11.2003 SigmaX 5.2 Release 3.7 3.33.9 Software 22.12.2003 SigmaX 5.2 Release 3.7 SP2 3.33.11 Software 27.01.2004 SigmaX 5.2 Release 3.7 SP3 3.33.13 Software 19.02.2004 SigmaX 5.2 Release 3.10 3.34.11 Software 21.04.2004 SigmaX 5.2 Release 3.11 3.34.11 Supplement 31.08.2004 SigmaX 5.2 Release 4.00 3.36.11 Software 16.12.2005 SigmaX 6.0.1 Release 4.00 SP2 3.36.16 Software 02 03 2006 SigmaX 6.0.1 Release 4.00 SP4 3.36.20 Software 23.05.2006 SigmaX 6.0.1 Release 4.01 3.37.08 Software 07.09.2006 SigmaX 6.0.1 Release 4.01 SP1 3.37.09 Software 26 09 2006 SigmaX 6.0.1 Release 4.01 SP3 3.37.12 Software 20 10 2006 SigmaX 6.0.1 Release 4.01 SP4 3.37.13 Software 13 08 2006 SigmaX 6.0.1 Release 4.01 SP4a 3.37.16 Software 17 11 2006 SigmaX 6.0.1 Release 4.01 SP5 3.37.18 Software 05 01 2007 SigmaX 6.0.1 Release 4.02 3.39.09 Software 26 01 2007 SigmaX 6.0.1 Release 4.03 3.40.06 Software 06 06 2007 SigmaX 6.0.1 Release 4.03 Sp1 3.40.09 Software 09 08 2007 SigmaX 6.0.1 Release 4.04 3.41.14 Software 27.02.2008 SigmaX 6.0.1 Release 4.04 SP1 3.41.15 Software 09.05.2008 SigmaX 6.0.1 Release 4.04 SP2 3.41.16 Software 15 09 2008 SigmaX 6.0.1 Release 4.04 SP3 3.41.18 Software 08 01 2009 SigmaX 6.0.1 Release 4.04 SP4 3.41.19 Software 08 01 2009 SigmaX 6.0.1 Release 4.05 3.42.34 Software 06 11 2009 SigmaX 6.0.1 Release 4.05 SP1 3.42.43 Software 22 03 2010 SigmaX 6.0.2 Release 4.05 SP2 3.42.48 Software 26.08.2010 SigmaX 6.0.2 Release 4.05 SEB 3.43.18 Software 08 12 2010 SigmaX 6.0.2 Release 4.06 3.44.14 Software 01 12 2011 SigmaX 6.0.2 Release 4.06 SP1 3.44.16 Software 01 12 2011 SigmaX 6.0.2 Release 4.06 SP1 3.44.18 Hotfix 01 02 2012 SigmaX 6.0.2 Release 4.07 3 45 48 Software 20 08 2012 SigmaX 7.0.6 Release 4.07 SP1 3 45 51 Service Pack 09 12 2012 SigmaX 7.0.6 Release 4.07 SP2 3 45 58 Service Pack 20 12 2013 SigmaX 7.0.6 Release 4.08 3.46.57 Software 10 04 2014 SigmaX 7.0.7 Release 4.08 3.46.62 Hotfix 21.05.2014 SigmaX 7.0.7 Release 4.08 3.46.70 Hotfix 23 07 2014 SigmaX 7.0.7 Release 4.08 3.46.72 Hotfix 04 08 2014 SigmaX 7.0.7 Release 4.08 3.46.73 Hotfix 12 08 2014 SigmaX 7.0.7 Release 4.08 3.46.79 Hotfix 08 10 2014 SigmaX 7.0.7 Release 4.08 (**1) 3.46.80 Software 10 04 2014 SigmaX 7.0.7 Release 4.08 3.46.81 Hotfix 17 02 2015 SigmaX 7.0.7 Release 4.08 3.46.85 Hotfix 19 03 2015 SigmaX 7.0.7 Release 4.08 3.46.86 Hotfix 19 03 2015 SigmaX 7.0.7 Release 4.08 (**2) 3.46.89 Software 10 04 2014 SigmaX 7.0.7 Release 4.08 3.46.98 Hotfix 14 12 2016 SigmaX 7.0.7 Release 4.08 (**3) 3.46.104 Software 28 02 2017 SigmaX 7.0.9 Release 4.08 3.46.105 Hotfix 10 03 2017 SigmaX 7.0.9 Release 4.08 (**4) 3.46.106 Software 28 03 2017 SigmaX 7.0.9 Release 4.08 3.46.107 Hotfix 08 08 2017 SigmaX 7.0.9 Release 4.08 3.46.108 Hotfix 01 05 2018 SigmaX 7.0.9 Release 4.08 (**5) 3.46.110 Software 13 05 2019 SigmaX 7.0.9 Release 4.08 (**6) 3.46.111 Hotfix 15 11 2019 SigmaX 7.0.9 Release 4.08 (**7) 3.46.131 Software 29 01 2020 SigmaX 7.0.9 Notes:   **1 Sigma build 4.46.57 with StruxureWare Building Operation v1.5 or 1.6 transition support program installed. **2 Sigma build 4.46.57 with StruxureWare Building Operation v1.8 transition support program installed. **3 Sigma build 4.46.57 with StruxureWare Building Operation v1.9 transition support program installed. **4 Sigma build 3.46.57 with StruxureWare Building Operation v2.01 transition support program installed. **5 Sigma build 3.46.57 with StruxureWare Building Operation v3.0.1, v3.0.2 and v3.0.3 transition support program installed.. **6 Sigma build 3.46.57 with StruxureWare Building Operation v3.0.4, v3.1 and v3.2 transition support program installed. **7 Sigma build 3.46.57 with StruxureWare Building Operation v3.2 or later transition support program installed.   Notes: 1. SigmaX version 7.0.9 is now available and can be used on any Sigma version that supported SigmaX version 7.0.6. 2. This information can be downloaded as a PDF file: Sigma Build Numbers 2023 3. When SigmaX 6.0.2 is installed, the build information provided by Sigma (Help > About) can be wrong (later than the actual version). This arises because SigmaX installs a file with Build 3.42.47 in the c:\sigma\bin folder. This is only a problem prior to Sigma Release 4.05 SEB.
View full article
Picard Product_Support
‎2021-01-07 05:36 AM

Last Updated: Gary Schneider Alumni (Retired) ‎2023-04-28 02:32 AM

Labels:
  • Satchwell BAS & Sigma
4539 Views

Using telnet command to check for open ports

Issue Checking if a port is open Product Line Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices, Pelco, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment TCP/IP Communication Command Prompt Telnet Command Cause Suspect certain network ports are blocked and need to verify Resolution It is possible to check if a port is open in a network by issuing the Telnet command. Note:- Telnet operates using the TCP protocol. UDP connectivity cannot be tested using Telnet. If a port is open, a blank screen will be seen after issuing the command: telnet [domainname or ip] [port] where [domainname or ip] is the domain name or IP address of the server being checked [port] is the port number the server application is listening on For example: telnet 192.168.0.20 9001 (to a closed port would display a connect failed message)   telnet 192.168.0.20 9003 (to an open port would display a blank screen)   To exit the Telnet session, type Ctrl + ] and then type "quit".   For how to enable Telnet in Windows 7 please see Enable Telnet Client on a Windows 7 PC
View full article
Picard Product_Support
‎2018-09-11 05:57 AM

Last Updated: Admiral GavinHe Admiral ‎2023-02-23 06:32 AM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
9270 Views

Problem uninstalling software

Issue Removing software from a PC may leave behind unused / old registry entries and folders from the removed software, this in some cases may prevent software re-installation Product Line Andover Continuum,EcoStruxure Building Operation,Satchwell BAS & Sigma,Satchwell MicroNet,TAC INET,TAC Vista Environment All supported Operating Systems Cause This is due to the windows uninstall program not fully removing all elements for the software. Some of this is due to windows thinking the the software may have been removed unintentionally and therefor all the previous settings will still be saved in case of  re-installation. For example, when SQL is uninstalled the program folders that contain the database will remain intact. This may be an issue if, for example, the software is removed due to a problem with the original installation. This is when a complete removal off all components and registry entries may be needed. Resolution The best solution for removing all the unused registry entries is to use a program designed to remove obsolete registry entries and temporary files. Some examples of these are: CCleaner, which will allow you to clean up your PC by removing past installation components. Revo Uninstaller  which is useful for removing redundant folders / files / Registry entries.   It may be useful to use both of these programs to ensure a complete cleanup. Revo Uninstaller can be used to remove unused software and then CCleaner to get rid of all the Temp files etc.  Finally remove the relevant folders from within the windows explorer, Example: C:\Program Files (x86)\Continuum Once done you should then be able to install a fresh clean copy of the application software. This solution is current in all versions of Windows including windows 10  
View full article
Picard Product_Support
‎2018-09-06 03:29 PM

Last Updated: Administrator CraigEl Administrator ‎2022-11-13 09:32 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
4609 Views

How to disable Sigma controller offline hardware and other Alarm

Issue Unwanted hardware and other alarms received at Enterprise Server Product Line Satchwell BAS & Sigma, EcoStruxure Building Operation Environment EcoStruxure Building Operation Sigma Release 4_08 (Build 3_46_57) Cause Unwanted Sigma hardware and other alarms received at Enterprise Server. Resolution Navigate through the “Sigma interface”, to the controller (OSN) that the alarms need to be disabled from. Select the controller’s property (basic tab), Device monitoring can be enabled or disabled.     If you need to disable the alarms for multiple controllers, this can be done by multi selecting the required controllers, opening the property panel and change the setting there.  
View full article
Gary Schneider Alumni (Retired)
‎2022-10-02 05:18 PM

on ‎2022-10-02 05:18 PM

Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
986 Views

Sigma IC3-Modbus 16bit, 32bit & 64 bit data type Compatibility

Warning   Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Confirming compatible Modbus data types available for a Sigma IC3 Modbus Product Line Satchwell Sigma Environment Sigma Release 4_05-SEB (Build 3_43_18) Sigma Release 4_05-SP2 (Build 3_42_48) Sigma Release 4_06 (Build 3_44_14) Sigma Release 4_06 SP1 (Build 3_44_16) Sigma Release 4_07 (Build 3_45_48) Sigma Release 4_07-SP1 (Build 3_45_51) Sigma Release 4_07-SP2 (Build 3_45_58) Sigma Release 4_08 (Build 3_46_57) IC3 Modbus Cause The use of 64-bit is not mentioned in documentation Resolution 16-bit registers are supported with all versions of Sigma. From Sigma release 4 05 SEB (Build 3_43_18) 32-bit registers are supported. 62-bit registers are not supported with Sigma IC3.   The ba077 Modbus 32-bit application note provides information on the engineering of 32-bit registers. https://ecoxpert.se.com/search?documentUUID=74eaf0dd-fbd9-4429-9c82-eb205aa9be07&title=BA077%20Modbus%2032%20Bit%20Values%20-%20Satchwell%20-%20Application%20Note Sigma 4.06 IC3 Modbus Firmware and Release Note https://ecoxpert.se.com/search?documentUUID=cb99b073-d9ab-400e-8e67-2f8343447768&title=Sigma%204.06%20IC3-Modbus%20Firmware%20-%20Release%20Notes Sigma IC3 Modbus 1.n.2 firmware is the latest available version https://ecoxpert.se.com/search?documentUUID=02d88785-9d13-4184-b74a-d1a0b5ce7edd&title=Sigma%20IC3%20Modbus%201.n.2%20-%20Firmware    
View full article
Gary Schneider Alumni (Retired)
‎2022-09-23 07:50 PM

on ‎2022-09-23 07:50 PM

Labels:
  • Satchwell BAS & Sigma
790 Views

Sigma IC Lon Values going on and offline

Issue Troubleshooting Sigma IC LON Values going on and offline Product Line Satchwell Sigma Environment Sigma Release 4_05-SEB (Build 3_43_18) Sigma Release 4_05-SP2 (Build 3_42_48) Sigma Release 4_06 (Build 3_44_14) Sigma Release 4_06 SP1 (Build 3_44_16) Sigma Release 4_07 (Build 3_45_48) Sigma Release 4_07-SP1 (Build 3_45_51) Sigma Release 4_07-SP2 (Build 3_45_58) Sigma Release 4_08 (Build 3_46_57) IC LON Cause Lon Values going into and out of default Resolution Compare the IC-LON’s Receive heartbeat set in the “gateway.txt” file in the IC-LON controller, to the send heartbeat set in the controller. The recommendation is for the receive heartbeat be set to 2-5 times the send heartbeat of the field controller. Starting at 2 times, then increasing if the problem persists. If the controller doesn’t have a heartbeat and the LON value rarely changes, disable the receiver heartbeat in the IC-LON’s gateway.txt file by setting the heartbeat to 0. Example: 1     2     3        4      5   6  7 2,   2,  112,  1293,  0,  0, 0   The Sigma system is now out of its support period, consideration should be given to transitioning or upgrading to SpaceLogic - EcoStruxure Building Operation.
View full article
Gary Schneider Alumni (Retired)
‎2022-09-23 07:48 PM

on ‎2022-09-23 07:48 PM

Labels:
  • Satchwell BAS & Sigma
645 Views
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 24
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of