Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

EasyLogic and SpaceLogic Controllers & RP-IO Modules as BACnet MS/TP third-party devices

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • EasyLogic and SpaceLogic Controllers & RP-IO Modules as BACnet MS/TP third-party devices
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2653 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EasyLogic and SpaceLogic Controllers & RP-IO Modules as BACnet MS/TP third-party devices

Guinan RobertAndriolo Guinan
‎2023-09-21 12:45 AM

Issue

Can the EasyLogic range of controllers & RP-IO Modules work under Building Operation 3.2 as BACnet MS/TP third-party devices 

Product Line

EcoStruxure Building Operation

Environment

  • EasyLogic Controllers, EasyLogic RP-V, EasyLogic RP-C, EasyLogic MP-C
  • EasyLogic RP-IO
  • SpaceLogic Advanced, Pro, and Pro Plus Controllers that support native BACnet MS/TP (via a SpaceLogic RS-485 Adapters.  

Cause

The documentation states that EasyLogic Controllers can be used as a Native BACnet MS/TP device. These devices must be configured using their respective supported Building Operation versions, such as Building Operation 2022 and above. However, there are no guidelines on whether they can be used as a third-party BACnet device, in particular in earlier versions such as Building Operation 3.2.   

Resolution

EasyLogic controllers can be used as BACnet MS/TP third-party party devices in Building Operation 3.2 since the EasyLogic range of RP and MP controllers, and RP-IO I/O modules natively communicate using the BACnet MS/TP protocol.  This same concept applies when using the devices as true 3rd-party devices (e.g., with Continuum and I/A systems) when older controllers fail, and these EasyLogic controllers are used as temporary replacements before a full transition.

 

What MUST be understood before taking this approach is that there is no automatic conversion when migrating the site (and devices) to later Building Operation versions that support these devices natively. After the upgrade, the controller must be deleted from the database and hosted as a native EBO controller.

 

During this process, some programming may be lost. This risk may be mitigated by creating Custom Types for the application once engineered in Building Operation 2022 (or higher) to future-proof the site for upgrades.  Using the latest firmware for the EasyLogic range of devices is also recommended.  

 

Furthermore, the SpaceLogic Controller Range that supports native BACnet MS/TP (via an RS-485 Adapters) can be configured in the same fashion as described for the EasyLogic range.

 

Refer to Hardware Overview for further details on each product line. 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (2)
  • Find more articles tagged with:
  • RobertAndriolo23
  • RobertAndriolo24
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of