Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84437members
353635posts

Surge Protection outlets

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
Mobius_apc
Ensign
Ensign
0 Likes
4
143

Surge Protection outlets

The manual for my most recent UPS (BR1500MS2) says the surge protection outlets are useful for printers, scanners, etc. (items which don't require battery backup).  BUT, I seem to recall reading somewhere (likely in these forums), that they should not be used for laser printers.  Is that correct?

Tags (1)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
3
125

Re: Surge Protection outlets

@Mobius_apc 

 

Correct. The issue with a laser printer is that when it starts a print, there is an inrush of current for warm-up. That inrush can cause a UPS to fault with an overload or prematurely fail.

The recommendation is to put the laser printer on a surge protector and depending on the printer, on a separate circuit.

See Answer In Context

Tags (1)
4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
3
126

Re: Surge Protection outlets

@Mobius_apc 

 

Correct. The issue with a laser printer is that when it starts a print, there is an inrush of current for warm-up. That inrush can cause a UPS to fault with an overload or prematurely fail.

The recommendation is to put the laser printer on a surge protector and depending on the printer, on a separate circuit.

Tags (1)
Mobius_apc
Ensign
Ensign
0 Likes
0
122

Re: Surge Protection outlets

Thanks, Bill.  Good to know the reason why, rather than just "Don't do that!".  🙂

Tags (1)
Mobius_apc
Ensign
Ensign
0 Likes
1
101

Re: Surge Protection outlets

A followup question:  is it okay (I presume it is) to plug in a laser printer to the other half of the same wall outlet the UPS is plugged into?

Tags (1)
BillP
Administrator Administrator
Administrator
0 Likes
0
61

Re: Surge Protection outlets

@Mobius_apc 

 

Yes. However, when the laser printer starts, and there is an inrush, it could temporarily cause the UPS to switch to battery. If that happens, you could correct the issue by adjusting the transfer voltage, but if the draw causes the voltage to drop too low, you would need to connect the printer to a different circuit.