when does a UPS shut off if there are multiple PCNS clients?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • when does a UPS shut off if there are multiple PCNS clients?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

0 Likes
3
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

when does a UPS shut off if there are multiple PCNS clients?

Let's say I have two physical servers plugged into a Smart-UPS with a NMC. Both servers have PCNS installed and configured to shut down the UPS after performing a graceful shutdown (in v4.2 Shutdown Settings -> UPS Shutdown: Turn off the UPS).

However, both servers have different shutdown periods: server A takes 3 minutes to shutdown, and server B takes 10 minutes to shut down. In this case, if the UPS starts to shutdown after given the instruction by server A, then server B is in for a real bad time.

What regulates this? How can I make sure that all servers are gracefully shutdown before the UPS does?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • pcns
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

0 Likes
0
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

Hi,

Sorry Smart-UPS 2200 is generic. We manufacture SMT2200, SUA2200, and SMX2200. Each model is unique and will react in a specific manor. You will find the exact model number on the bar code sticker on the back of the UPS.

To answer the basic question, you need to configure the NMC to provide power / not shutdown until the system with the longest shutdown cycle has completed. Lets say your Smart-UPS 2200 is an SUA2200. You need to set the low battery duration and or maximum required delay to be a minimum of 2 minutes greater than the needed shutdown delay. The diagram below from the PCNS User's Guide show the process.

So, if you configured PCNS to start a shutdown after the UPS has been on battery for 5 minutes once that delay has been met the OS will be commanded down and a signal will be sent to the NMC commanding the UPS down. At that time the UPS will wait the amount of time set in low battery duration or the maximum required delay which ever is greater. Then wait an additional 2 minute and finally wait and configured shutdown delay and then power will be cut to the outlets.

If your Smart-UPS 2200 is a SMT or SMX then the shutdown delay is based on the outlet groups delay.

The shutdown process is discussed in detail in the PCNS User's Guide starting on page 40 of the PDF.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

0 Likes
0
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

Hi,

What is the model of the UPS? Depending on the model the power off is based on the outlet groups or low battery / maximum required delay. It is not based on the amount of time the OS takes. You have to enter the proper time again depending on the model UPS. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

Thank you, this is a Smart-UPS 2200.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:53 AM . Last Modified: ‎2024-03-18 03:03 AM

Hi,

Sorry Smart-UPS 2200 is generic. We manufacture SMT2200, SUA2200, and SMX2200. Each model is unique and will react in a specific manor. You will find the exact model number on the bar code sticker on the back of the UPS.

To answer the basic question, you need to configure the NMC to provide power / not shutdown until the system with the longest shutdown cycle has completed. Lets say your Smart-UPS 2200 is an SUA2200. You need to set the low battery duration and or maximum required delay to be a minimum of 2 minutes greater than the needed shutdown delay. The diagram below from the PCNS User's Guide show the process.

So, if you configured PCNS to start a shutdown after the UPS has been on battery for 5 minutes once that delay has been met the OS will be commanded down and a signal will be sent to the NMC commanding the UPS down. At that time the UPS will wait the amount of time set in low battery duration or the maximum required delay which ever is greater. Then wait an additional 2 minute and finally wait and configured shutdown delay and then power will be cut to the outlets.

If your Smart-UPS 2200 is a SMT or SMX then the shutdown delay is based on the outlet groups delay.

The shutdown process is discussed in detail in the PCNS User's Guide starting on page 40 of the PDF.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of