Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82629members
350279posts

symmetra lx site wiring fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
ctferndo_apc
Crewman
Crewman
0 Likes
3
206

symmetra lx site wiring fault

This was originally posted on APC forums on 5/28/2009


I still get a site wiring fault even if L1 to N and L2 to N is less han 8%. In fact the difference is less than 1 volt. Please help.


Accepted Solutions
Erasmus_apc
Sisko
Sisko
0 Likes
0
206

Re: symmetra lx site wiring fault

This was originally posted on APC forums on 5/28/2009


The US unit is L1,L2,N,G only per the electrical installation guide, with no exceptions. The Philippines would use the 230v "I" model Symmetra LX which is designed to be used for H, N, G wiring.

See Answer In Context

3 Replies 3
Erasmus_apc
Sisko
Sisko
0 Likes
0
206

Re: symmetra lx site wiring fault

This was originally posted on APC forums on 5/28/2009


A site wiring fault can also be present if the UPS detects no neutral on the input. Additionally, if the input phases are derived from a separate panel/transformer than the neutral that is wired to the unit, this can cause intermittent site wiring faults as well.

Have you checked your system wiring configuration? Both phases, neutral and ground should be wired per this kbase: Answer ID 7059, which can be accessed via the following link:

http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7059

Your best bet at this point would be to totally de-energize the UPS and firmly reseat the wiring tray in the back of the unit and verify all wiring back to the panel and on the input to the unit.

Has this UPS worked fine in the past or is this a new installation?

ctferndo_apc
Crewman
Crewman
0 Likes
0
206

Re: symmetra lx site wiring fault

This was originally posted on APC forums on 5/28/2009


This is a new installation in the Philippines. But the unit is a US / Japan Symmetra LX 16KVA. We have a 230 volt single phase and I extracted neutral from earth ground which provided 115 v L1 to N and 115 V L2 to N.

Erasmus_apc
Sisko
Sisko
0 Likes
0
207

Re: symmetra lx site wiring fault

This was originally posted on APC forums on 5/28/2009


The US unit is L1,L2,N,G only per the electrical installation guide, with no exceptions. The Philippines would use the 230v "I" model Symmetra LX which is designed to be used for H, N, G wiring.