right configuration for Vmware Cluster with 2 different UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • right configuration for Vmware Cluster with 2 different UPS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:54 PM . Last Modified: ‎2024-03-12 12:58 AM

0 Likes
3
726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:54 PM . Last Modified: ‎2024-03-12 12:58 AM

right configuration for Vmware Cluster with 2 different UPS

Hi,

We have a cluster with 3 hosts in 2 different locations. 2 hosts (VH1 and VH3) in one location with an UPS1 and 1 host (VH2) with UPS2.

So on the first step we will monitor UPS2 and if the is a power event (on Battery)we want to migrate all VM's from host VH2 to the 2 additional ones hosts VH1 and VH3 and shutdown host VH2.

So we installed the Powerchute network shutdown on a physical Windows machine connected to UPS1.

Single UPS and vcenter connection.

We don't want to shutdown the Powerchute machine neither the UPS2.

So we enable on the virtualization settings just the VM Migration and Shutdown Settings "Don't turn off the UPS" and under host protection we just see VH2

Which event we have to setup to trigger the migration and the shutdown of the host?

When we enable the Shutdown when the UPS is on Battery, will then the migration start when the UPS2 goes to Battery?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:54 PM . Last Modified: ‎2024-03-12 12:58 AM

0 Likes
0
726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:54 PM . Last Modified: ‎2024-03-12 12:58 AM

Hi,

On 11/8/2017 10:07 AM, Juergen said:

So this means when I enabled the UPS on Battery shutdown event with a delay with 90 seconds. The whole migration process will when the UPS is on battery for more then 90 seconds and when the migration is finished the host will be shut down.

Correct. After the UPS has run on battery for 90 seconds PowerChute will begin the shutdown process. If migration has been configure the VMs will migrate and then the host will be commanded to power down. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:54 PM . Last Modified: ‎2024-03-12 12:58 AM

0 Likes
0
726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:54 PM . Last Modified: ‎2024-03-12 12:58 AM

Hi,

the recommended configuration is to install PowerChute Network Shutdown (PCNS) at each site. When the UPS at site 1 switches to battery the PowerChute client at site 1 will react. When the UPS at site 2 switches to battery the PowerChute client at site 2 will react. 

I recommend you review Application Note 180. Configuring for multiple sites is discussed starting on page 11.

Application Note 180 list both PCNS and vCenter running on Windows server at each location not as VMs on the host/s. You can install the PowerChute VM and you can install vCenter Server VM. If you do install PowerChute and vCenter VMs these VMs should not be migrated. Also, running vCenter as a VM and configured for multiple sites is not an officially support configuration.

On 11/7/2017 7:51 AM, Juergen said:

Which event we have to setup to trigger the migration and the shutdown of the host?

You can configure PowerChute to start the shutdown and migration processes after the UPS has been on battery for a set amount of time or when the UPS has a set amount of runtime remaining. Both these events are explained in the User's Guide starting on page 101 or by clicking on Help from within the PowerChute web interface. 

Configuring migration is discussed starting on page 26 of the User's Guide and also in Help. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:54 PM . Last Modified: ‎2024-03-12 12:58 AM

0 Likes
0
726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:54 PM . Last Modified: ‎2024-03-12 12:58 AM

So this means when I enabled the UPS on Battery shutdown event with a delay with 90 seconds. The whole migration process will when the UPS is on battery for more then 90 seconds and when the migration is finished the host will be shut down.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:54 PM . Last Modified: ‎2024-03-12 12:58 AM

0 Likes
0
727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:54 PM . Last Modified: ‎2024-03-12 12:58 AM

Hi,

On 11/8/2017 10:07 AM, Juergen said:

So this means when I enabled the UPS on Battery shutdown event with a delay with 90 seconds. The whole migration process will when the UPS is on battery for more then 90 seconds and when the migration is finished the host will be shut down.

Correct. After the UPS has run on battery for 90 seconds PowerChute will begin the shutdown process. If migration has been configure the VMs will migrate and then the host will be commanded to power down. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of