Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

"Failed to apply one or more values"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • "Failed to apply one or more values"
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
SW_apc
Ensign SW_apc
Ensign

Posted: ‎2021-06-30 07:09 PM

0 Likes
5
1729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:09 PM

"Failed to apply one or more values"

This was originally posted on APC forums on 3/25/2010


Hi all,

We have an issue with a UPS that is connected up to a server at a remote site. The UPS is a Smart-UPS 3000 RM, connected to an HP server running Windows Server 2003 5.2 and Powerchute Agent v8.0.0.306. We are running Powerchute Business Edition Deluxe v8.0 on our Server at Head Office. The UPS is connected to the remote server with one of the APC USB to 10P10C connectors.

When I am trying to make a change to the UPS through the console on my machine (in this case, trying to raise the high-transfer voltage reporting level to 257), I receive the error message:
"Failed to apply one or more values. Categories that contain failures are designated with a red icon in the category list. Items that failed are highlighted in red in the identified category pages."

The UPS is reporting in normally and appears to be functioning correctly, it's making all its reports as it should and is showing what appear to be the correct values on the Voltage Analysis page (it's slightly above the reporting value which is why I need to make this change).

If anyone has any ideas on how to resolve this, please let me know! 😉

Many thanks

Steve

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • communication
  • failed
  • issue
  • ups
  • values
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Admiral Techie_apc
Admiral

Posted: ‎2021-06-30 07:10 PM

0 Likes
0
1728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:10 PM

This was originally posted on APC forums on 4/7/2010


You should only use the cable that came with the UPS. My suspicious is that the cable that you are using is the cause of the issue. If possible, could you please use the cable that came with the UPS and see if this resolves?

See Answer In Context

Reply
Replies 5
juangele_apc
Lt. Commander juangele_apc
Lt. Commander

Posted: ‎2021-06-30 07:10 PM

0 Likes
0
1728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:10 PM

This was originally posted on APC forums on 4/5/2010


Hi Steve,

Before going any further, I would like to know if you are using any interface expander on your set up? How many computers do you want to receive shutdown signal in case of a power problem?

Reply
SW_apc
Ensign SW_apc
Ensign

Posted: ‎2021-06-30 07:10 PM

0 Likes
0
1729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:10 PM

This was originally posted on APC forums on 4/7/2010


Hi juangele,

No, we are not using an interface expander. The UPS is connected directly into the server using the 10P10C to USB cable. No other servers need to be sent shutdown signals at this site.

Steve

Reply
juangele_apc
Lt. Commander juangele_apc
Lt. Commander

Posted: ‎2021-06-30 07:10 PM

0 Likes
0
1729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:10 PM

This was originally posted on APC forums on 4/8/2010


Hi Steve,

Please ensure that the cable you are using is one that came with the UPS. Also, you may try using either the IP address of the computer or the computer name itself to add it on the console.

Try this as well Link:[kbase2596|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2596&p_created=1030565084&p...]

Please let me know if you still need further assistance.

Reply
Techie_apc
Admiral Techie_apc
Admiral

Posted: ‎2021-06-30 07:10 PM

0 Likes
0
1729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:10 PM

This was originally posted on APC forums on 4/7/2010


You should only use the cable that came with the UPS. My suspicious is that the cable that you are using is the cause of the issue. If possible, could you please use the cable that came with the UPS and see if this resolves?

Reply
SW_apc
Ensign SW_apc
Ensign

Posted: ‎2021-06-30 07:10 PM

0 Likes
0
1729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 07:10 PM

This was originally posted on APC forums on 4/13/2010


Hi all,

We had an engineer on site while doing his rounds the other day and I had him replace the cable - it looks like this was the cause of the fault. I can now do everything as I should be able to. It was a proper APC cable as well, I think it may have taken a knock at some point and broken a wire.

Thanks all for your input.

Steve

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc